Welder Electric Circuit Question

   / Welder Electric Circuit Question #1  

drm

Silver Member
Joined
Sep 22, 2004
Messages
235
Location
Western PA, North of Pittsburgh
Tractor
2004 NH TC33DA
I just purchased a Lincoln Power Mig 215. Now I need to run a new circuit to the garage to power it. Distance from circuit panel (200 amp capacity) is 100 feet. I will also make up a 40' +/- extension cord so I can move the welder around a little.

Lincoln's recommendations for the circuit is for a 60 amp fuse or breaker (Super Lag) and 8 AWG for runs over 100' for 75 C Copper wire in Conduit. The Input Ampere Rating on the Nameplate is 41 amps.

Running a voltage drop calculator for: Copper wire, 240 volt, 3% voltage drop, 60 amps, 140' length indicates to use a #4 conductor (good up to 194’ feet; #6 is good for up to 122’ conductor length calculator). For 41 amps the recommendation is #6 (good up to 178’ feet; #8 is good for up to 112’).

Why the difference? It is Friday night so I can not call Lincoln and I wanted to pick up supplies in the AM to get welding. Can any electricians or others in the know explain the difference?

Thanks
 
   / Welder Electric Circuit Question #2  
A welder is not going to be continuous but you should always use a bigger conductor as heat plays a part in what is going through the wire. I would run a #6 min and a #8-3 sow type cord for your welder. the rest is up to you. Also use a cord cap rated for your welder.
 
   / Welder Electric Circuit Question
  • Thread Starter
#3  
Lynkage said:
A welder is not going to be continuous but you should always use a bigger conductor as heat plays a part in what is going through the wire. I would run a #6 min and a #8-3 sow type cord for your welder. the rest is up to you. Also use a cord cap rated for your welder.

Can you tell me what a cord cap is?
 
   / Welder Electric Circuit Question #4  
Plug type.
I use twist lock's.
 
   / Welder Electric Circuit Question #5  
The standard 220v plug on welders is a NEMA 6-50P. The corresponding recepticle is a NEMA 6-50R. They are not twist lock and they are not comaptible with electric clothes dryers.

If you want the correct information you should ask your questions on one of the welding forums like the Hobart Welders. The forums are not brand specific and get questions like this all the time.

I wouldn't be asking tractor questions over there and I wouldn't be asking important welding questions here.
 
   / Welder Electric Circuit Question
  • Thread Starter
#6  
drm said:
Can you tell me what a cord cap is?

Now that I have some sleep, I am embarrassed that I asked that question. I know the receptacle type, like mad said NEMA 6-50R. I was incorrectly thinking that Lynkage was referring to a "CAP" type/rating of electrical wiring and not the Plug/Receptacle type.

Mad,

I have posted on the welding web website. Just a lot more traffic here and most likely any electrician that has run a welding circuit or that has a good bit of experience would be able to give some good guidance even if they do not weld.
 
   / Welder Electric Circuit Question #7  
The Hobart Welders forum is probably the most active welding forum out there. It is frequented by hobbyist and professionals alike. Wiring questions are asked and answered just about every other day. Welding Web is a relative new comer, so to speak, with no where near the traffic that Hobart has.
 
   / Welder Electric Circuit Question
  • Thread Starter
#8  
Mad,

I posted to Hobart site and got an answer already. Thanks for the suggestion.
 
   / Welder Electric Circuit Question #9  
You can use ANY plug rated for your application. Some people use twist lok some blade type. I just standardized all of my 220v tools so that I can buy and use one type of plug. This also corresponds to my generator and RV so this way in a pinch you can use what you need when you need it!;)
 
   / Welder Electric Circuit Question
  • Thread Starter
#10  
I was not able to get the electric supply this morning so I spent some time thinking about the situation. I have a sub panel for the pool in the opposite corner of the garage from where I want the welder. It is supplied with 96’ - #6 AL conductors and a 50 amp breaker at the main house circuit panel. Existing circuits in the pool sub-panel are: pool pump (20 Amp), lights (minimal), yard receptacle (20 amp), and heat pump (30 amp). It has 9 open spaces but is at already at capacity for load and wire size.

I am going to replace the 50 amp breaker in the main circuit panel with a 100 amp and use #4 copper or equivalent AL to service the panel (96’ run of cable) for the garage/pool/welder. I will use the existing #6 AL wire to service the welder (70’ run from panel). I will add 2 – 20 amp outlet circuits around the garage. I also need more lights in the garage so I will add 4 sets of 2 fluorescent 4' fixtures hung at about 10’ above the floor. I want these switched via three separate switches to control the area needing lit.

So for a little more than just adding one 50 amp outlet I will get the additional lighting and outlets. How does this sound?
 

Tractor & Equipment Auctions

378645 (A51573)
378645 (A51573)
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
2012 Chevrolet Silverado 2500HD Enclosed Service Truck (A52377)
2012 Chevrolet...
2016 TROXELL 130BBL VAC TRAILER (A52472)
2016 TROXELL...
Redirective Crash Cushion Guardrail (A51692)
Redirective Crash...
JOHN DEERE 5075GN LOT NUMBER 127 (A53084)
JOHN DEERE 5075GN...
 
Top