"The poster above using a 70A breaker on # 6 wire has great potential to set the wire/cord on fire before the breaker trips when operating long term at max output. #6 is only rated for 50A. 70A requires #4 or #2 which is not readily available in a SO cord arrangement."
Ron, I should have clarified this more, sorry - I'm aware of the numbers - in this case, it's an old Zinsco box and I couldn't find a 50 amp breaker for it, I already had the SO cord, that circuit NEVER will see more than 50 amps INRUSH when the 5 horse Baldor starts the compressor, the duty cycle of the ONLY welder that might draw more than 30 amps ALREADY excludes enough wire heating to NOT be a problem (the rest are all inverter technology) -
The maximum SUSTAINED load on the circuit with compressor running (23 amps) and any of the welders running, would be around 55 amps. Even that would only happen for a couple minutes, since this compressor comes up to pressure from cut-in to cut-out in about 90 seconds.
When I get the time, the old Zinsco breaker box will be replaced - at that time, the SO cord, 70 amp breaker, and any other "temp" stuff will also go "bye-bye".
To any who may want to duplicate what I did,
DON'T !!?!
- I am the ONLY one in this household who will EVER use this setup, I know the REAL capabilities, and I will be replacing any and all "iffy" components when I remodel and re-wire.
Ron (Tractor SeaBee) has given you the RIGHT way - please follow his numbers if you wire your own... Steve