Hey Folks,
The continuing saga ........continues. Sailfast, I will continue with my efforts. No way am I in over my head, it will get done just fine.
Woke up at 0430 and the house was 89. I figured it was the coal stove putting out that heat and the outside temp rose to 35. A little while later I was working in the basement, and I saw that zone 4 (DHW) was lit up. I thought no problem, I just got out of the shower and it is refilling/heating the storage tank. Half an hour later, it's still running.
Here is what I noticed. Boiler display said central heat was on (still 88 upstairs, t-stat set 68). Boiler circulator was on, system circulator was on, and DHW circulator was on. The loop manifolds were warm, mix valve temperature was 130. However, the circulators at the manifolds were quiet.
I did a number of temp changes to no avail. I disconnected the outside temp sensor. This started out with boiler set temp at 140, and it supplied the mixer valves at 130 dead nuts. To fix it, I rewired the circulators back to original, then changed temps back to original. My next step is to leave everything wired as is, and adjust the temps again. If that holds, I have to look at the zone rewiring again.
Here's what the display read at one random point. (Remember, CH, System, and DHW circulators running)
CIRCULATOR STATUS/CYCLES
System circulator. ON
Boiler circulator. ON
DHW. ON
HEAT DEMAND
CH. ON
DHW. OFF
AUX HEAT. OFF
FROST PROTECTION. OFF
BOILER
SUPPLY. 140
SET POINT 140
RETURN. 134
RATE. 23%
PRIORITY. CH
STATUS. RUNNING
STACK. 145
The continuing saga ........continues. Sailfast, I will continue with my efforts. No way am I in over my head, it will get done just fine.
Woke up at 0430 and the house was 89. I figured it was the coal stove putting out that heat and the outside temp rose to 35. A little while later I was working in the basement, and I saw that zone 4 (DHW) was lit up. I thought no problem, I just got out of the shower and it is refilling/heating the storage tank. Half an hour later, it's still running.
Here is what I noticed. Boiler display said central heat was on (still 88 upstairs, t-stat set 68). Boiler circulator was on, system circulator was on, and DHW circulator was on. The loop manifolds were warm, mix valve temperature was 130. However, the circulators at the manifolds were quiet.
I did a number of temp changes to no avail. I disconnected the outside temp sensor. This started out with boiler set temp at 140, and it supplied the mixer valves at 130 dead nuts. To fix it, I rewired the circulators back to original, then changed temps back to original. My next step is to leave everything wired as is, and adjust the temps again. If that holds, I have to look at the zone rewiring again.
Here's what the display read at one random point. (Remember, CH, System, and DHW circulators running)
CIRCULATOR STATUS/CYCLES
System circulator. ON
Boiler circulator. ON
DHW. ON
HEAT DEMAND
CH. ON
DHW. OFF
AUX HEAT. OFF
FROST PROTECTION. OFF
BOILER
SUPPLY. 140
SET POINT 140
RETURN. 134
RATE. 23%
PRIORITY. CH
STATUS. RUNNING
STACK. 145