Veteran Member
If you want 125 amps of power at 3% voltage drop for a 125' in conduit using 220v you would need 1/0 in copper. To use a #4 copper wire you could still use the 125 amp panel, but would need to install a 70 amp breaker in the feeder panel. So you can actually go a bit bigger than the proposed 60a breaker. There is no need to use a smaller breaker in the sub panel as that main breaker is only serving as a disconnect.