Link to NC plumbing code on this topic:
http://ecodes.iccsafe.org/nxt/gateway.dll/Plumbing/chapter01246/section%20head01247/subsection01248.htm?fn=main-nf.htm$f=templates$3.0
"Notches on the ends of joists shall not exceed one fourth the joist depth. Holes bored in joists shall not be within 2 inches (51 mm) of the top or bottom of the joist, and the diameter of any such hole shall not exceed one third the depth of the joist. Notches in the top or bottom of joists shall not exceed one sixth the depth and shall not be located in the middle third of the span."
Davitk's rule agrees but holes and notches are not the same thing i.e. properly placed holes in the center 1/3 are permissable, notches are not. The principles in play are that bending stress is highest at the center of a span and that the top and bottom fibers of the joist carry the majority of the stress.
Check the code in your state.
http://ecodes.iccsafe.org/nxt/gateway.dll/Plumbing/chapter01246/section%20head01247/subsection01248.htm?fn=main-nf.htm$f=templates$3.0
"Notches on the ends of joists shall not exceed one fourth the joist depth. Holes bored in joists shall not be within 2 inches (51 mm) of the top or bottom of the joist, and the diameter of any such hole shall not exceed one third the depth of the joist. Notches in the top or bottom of joists shall not exceed one sixth the depth and shall not be located in the middle third of the span."
Davitk's rule agrees but holes and notches are not the same thing i.e. properly placed holes in the center 1/3 are permissable, notches are not. The principles in play are that bending stress is highest at the center of a span and that the top and bottom fibers of the joist carry the majority of the stress.
Check the code in your state.