not really sure what gauge yet, but i am sure it will be pretty heavy. i am going to run lights to my horse arena, and havnt really got to talk to a electrician yet, to get input on wire size, etc. i probably have 300 or more ft to run. its a spring project, so not that big deal yet, just thought i would start getting some ideas on burying the wire in advance. thanks for all the help guy
 
   / burying wire with subsoiler advice
  • Thread Starter
#13  
hey schism, we are close to st louis as well. hour west or so in mo. just saying hey and thanks for the your link
 
   / burying wire with subsoiler advice #14  
hey schism, we are close to st louis as well. hour west or so in mo. just saying hey and thanks for the your link

howdy!... welcome to the site.
 
   / burying wire with subsoiler advice #15  
Generaly your conduit size should be 60% larger than the diameter of the cable, 40% fill is NEC. Regardless of cable size I typicaly do not install conduit more than 200 ft without a pull box and with no more than 3 90 deg bends.
 
   / burying wire with subsoiler advice #16  
I think the wire would have to be a larger gauge to avoid voltage drop if it's a 300' run. I had seen the earlier posts about burying cable with a subsoiler, but I appreciate it being brought back up to get more of the details.

Could you bury cable 18" with a subsoiler if you only have a 22 hp tractor or does it take a larger tractor?
 
   / burying wire with subsoiler advice #17  
I think the wire would have to be a larger gauge to avoid voltage drop if it's a 300' run. I had seen the earlier posts about burying cable with a subsoiler, but I appreciate it being brought back up to get more of the details.

Could you bury cable 18" with a subsoiler if you only have a 22 hp tractor or does it take a larger tractor?

I couldn't find my code book but if the foggy old brain works you need 12 gauge minimum for 300" and 15 amps, 10g would be better depending on total amp load plus current drop for the distance.
You might consider using 12/3 with ground, that will give you 2 separate circuits in one wire and pull.
I'm sure that theres a master electrician out there that will give us the correct info/specs.

As far as pulling the subsoiler 18" dep with 22hp, its doable ,depends on 2 things; traction and soil type. I've pulled my CK 20 HST 12-18" deep in one pass in sandy loam. In heavy clay Ive had to make 2 or 3 passes to get full 18". Of course roots and rocks don't count.

Have fun. Joe
 
   / burying wire with subsoiler advice #18  
I couldn't find my code book but if the foggy old brain works you need 12 gauge minimum for 300" and 15 amps, 10g would be better depending on total amp load plus current drop for the distance.
You might consider using 12/3 with ground, that will give you 2 separate circuits in one wire and pull.
I'm sure that theres a master electrician out there that will give us the correct info/specs.

As far as pulling the subsoiler 18" dep with 22hp, its doable ,depends on 2 things; traction and soil type. I've pulled my CK 20 HST 12-18" deep in one pass in sandy loam. In heavy clay Ive had to make 2 or 3 passes to get full 18". Of course roots and rocks don't count.

Have fun. Joe

There have been many disagreements on here about this exact 300' of wire scenario.

You need to calculate your load, and then size the wire so that the voltage drop is acceptable.

Most will agree that even with a small load, (over 700 watts), #12 falls below the minimum requirements for this job, due to the voltage drop, if your doing it by the book,

If you just want to run some incandescent lights only, say 600 watts max, they will handle the drop & #12 wire can work.

If you want to have say 1000 watts max, you need at least #10.

#8 or better, will get you 12 amps, at 115 volts.

#6 does not even give you a full 20 amps at 300 feet, without a drop to 114 volts, assuming you have 120 volts to start with, many don't.

You really want to run it in conduit, and that also has to be sized properly to keep the wire from over heating.

Most electricians will urge you to run even larger wire now, rather than regret it later.
 
   / burying wire with subsoiler advice
  • Thread Starter
#19  
hey guys, thanks so much for taking the time to give me such useful detailed advice. the more i read, i think this might be one of those projects left to the pros, or at least get a certified electrician, to come out and look at the job, and tell me what would be better for this application. thanks again so much
 
   / burying wire with subsoiler advice #20  
Here's a good voltage drop calculator where you can plug in whatever variables/choices you have...It's interesting to see the what different wire types does, etc...

BotaKix...Na, I would think it out and do it yourself. You got the tools, information and TBN.

Voltage Drop Calculator
 
 