i can see that most of you like your geothermal systems.......my experience here in north Idaho have been mixed.
It must be the way they install it here, cause all 3 people that have had it installed that i have had contact with arnt happy with the systems.
The reason i have been involved is im there wiring in an electric water heater or boiler to supplement their winter heat.
There FREEZING. Maybe our subsurface temps are too cold????
Proper design is a must if it's going to work right, and retrofits aren't easy to make work in some cases.
For example, hot water baseboard heaters don't work well with geothermal, simply because the water doesn't get hot enough. My hottest water temp at -20 C outside temp is just under 100 F. That's not hot enough for baseboard heaters to keep the house warm. It
is hot enough for infloor piping, though.
If you already have infloor piping for radiant heat, what is the spacing? Mine is every 6", not 12" as is common with higher temp systems. We discussed it with the installers at the time we built the house, they were undecided if 12" spacing was going to be enough, so erred on the side of caution and went with 6" throughout, with the garage floor being the exception. It has 12" spacing, and is harder to keep warm. Mind you, it also has a 7x10 steel garage door with an R value of around 12, so that's a source of heat loss to begin with.
In my personal opinion, geothermal is a much better option for new construction than retro-fit, the cost is more reasonable since you're comparing the complete package price instead of simply adding a different thermal source. It'll never compare well with an oil furnace for initial cost.
Our costs were about $5000 more than anything else that was even vaguely energy efficient, for the whole project.
If I had to guess, I'd say there was a miscalculation when those systems you mentioned were designed, either in the size of the system, or in the application of the heat generated. Possibly in the heat loss numbers for the house.
We had three estimates, one was for a 5 ton system, the one we went with was a 3 ton. The 3 ton does a good job, so the 5 would have been overkill.
This is relatively new to most installers, I expect the knowledge base will get better with time and experience.
Sean