I know this is an old thread but it contains great info! I'm considering burying about 900 feet of romax for a gate at the end of my driveway. I'm guessing the best scenario would be for the romax to be inside of a flexible (PVC or other pex-like) conduit?
However, I doubt you would be able to string romax through 900 feet of conduit before laying in the ground. That has to be nearly impossible. Am I wrong?
I'm assuming I'm looking a direct burial of the romax?
for a 900 foot run, your going to have a tremendous voltage drop with a wire run. In the past (I'm an electrical contractor) we have run triplex aluminum wires direct buried in ground 24" below surface for runs like your describing. I would run a #4/#4/#2 urd (DIRECT BURY ALUM) run to get clean 20 amp at the end of the run. I know #4 alum seems too large, but it will afford a 10% voltage drop
if you use #12 copper wire, you would have a 57% voltage drop at the end, meaning instead of 120 volt you'd be getting about 52 volts.
with the #4 alum your could expect between 105 - 110 volts, which falls in the acceptable range.
Also, the #4 triplex is comparably priced to 10/2 UF romex...probibly even cheaper nowdays due to tremendous Price increase in copper.
while your at it, throw in direct burial phone cable for comm port to the gate.....or better yet....lose the gate hehe
i truly hate those pesky gates. there always miles from the house and power. The wireless intercoms are always picking up transiant radio stations, etc. there always a pesty install.