Hey what is 300 mcm? that is what it says I need for my barn.
Hey what is 300 mcm?
Nope not anymore.. that is old code,,,
2 code problems,, you do have is the wire needs to be in pipe all the way to the panel.. and you need a Main breaker..
Nope not anymore.. that is old code,,,2 code problems,, you do have is the wire needs to be in pipe all the way to the panel.. and you need a Main breaker..
Yeiks...thats some spendy wire. How many feet you going to need. I ran 350 MCM to my shop, but the run was 350 feet and I'm using 200 amps. I did this about 4 years ago, and it was expensive back then. Currently its running $1.35 per foot for each run. You would need 2 runs of this and a downsized neutral (250 MCM) run Plus a #6 ground. I personally run my neutral the same size as the main conductors, but you can drop it to the next size down.
I ran 3-1/2" conduit for ease of installation, as it is legal to go 3" but a pain to pull in it. You'll not find this wire at Home Depot....best locate an electrical wholesale house nearby.
What distance are you looking to run, and what amperage
A better calculator to use would be this one
Voltage Drop Calculator
It allows you to adjust for voltage drop. For me if i used the previous posters calculator i would have needed to use 500 MCM wire, but i allowed myself a 3% voltage drop (acceptable) and only needed to use 350 MCM wire using this calculator or the formulas in my NEC book.
By the way, they figure a circuit as a loop (up and back) so the figure for 1/2 the circuit distance means the length from the main panel to the sub panel - one direction
I was at Lowes the other day and their chart says I needed 1/0 copper for 200 amp service and I almost passed out when I figured out what I needed would cost. Now I find out I need to go bigger and the way it looks I'll have more in the wire than I do in the lumber so far.
Without looking it up that is what I would have come up with. I put a service in my new pole barn a few weeks back and I needed a local ground rod. Years ago I don't believe it would have been a requirement.you DO need a single ground rod per 2008 and 2011 code book for a panel in a separate building. Also need the 4 wire run from main panel to subpanel, and yes a main breaker is required in a separate buildings panel.
Without looking it up that is what I would have come up with. I put a service in my new poll barn a few weeks back and I needed a local ground rod. Years ago I don't believe it would have been a requirement.