Welder Extension Cord

   / Welder Extension Cord #21  
he could plug that thing into a 115v 15 amp circuit if he wanted to, you can always use a wire thicker then needed, but never thinner. I used to have my welder plugged into a 30 amp circuit, with a 25 foot 4/3 cord, thats way better than the 10/3 needed, much less voltage drop.

I think this is correct. The critical thing is that the fuse blows before the wire glows.
 
   / Welder Extension Cord #22  
Mine is 8/3 wire. I am assuming in my situation I should be fine. What is your opinion?

I am sure you will be fine. My outdated code book says 8 gauge is for up to 60 amps. I was actually going to get 20 feet of 6 or 8 gauge for my welders cord, but because of a mistake by the new guy at the cable store, we got 25 feet of 4 gauge for like $40-$50. If I had to pay the full price for the cable, no way would I use 4 gauge, 6 at the most. (this thing is HEAVY)
 
   / Welder Extension Cord #23  
I am sure you will be fine. My outdated code book says 8 gauge is for up to 60 amps. I was actually going to get 20 feet of 6 or 8 gauge for my welders cord, but because of a mistake by the new guy at the cable store, we got 25 feet of 4 gauge for like $40-$50. If I had to pay the full price for the cable, no way would I use 4 gauge, 6 at the most. (this thing is HEAVY)


60 amp Canadian is 40 amps US :). THHN wire #8 is rated 40 amps @ 60C (140F) which is how they rate extension cords. If you use the 90C tables, it goes to 59 amps, but no one recognizes that temp range for cables.
 
   / Welder Extension Cord #24  
60 amp Canadian is 40 amps US :). THHN wire #8 is rated 40 amps @ 60C (140F) which is how they rate extension cords. If you use the 90C tables, it goes to 59 amps, but no one recognizes that temp range for cables.

I am sure you know far more about this then I do, and I am sure you are right. I was looking at the table some more, and it is for loomex cable, and is based on a spec sheet from 1982. (this isnt the offical code book, just a simplified version, based on the offical version)
 
   / Welder Extension Cord #25  
I am sure you know far more about this then I do, and I am sure you are right. I was looking at the table some more, and it is for loomex cable, and is based on a spec sheet from 1982. (this isnt the offical code book, just a simplified version, based on the offical version)

i wish they would bring back the old 1970's code books . they were like 1/4" thick hehe. My new code book is about 2" thick..all of it useless garbage :laughing: :laughing: :laughing: :laughing: :laughing: :laughing:. Its amazing how the 1950 houses are running just fine thank you
 
   / Welder Extension Cord #26  
Welder circuits and extension cords can be Derated a little bit due to the duty cycle of welders, meaning they are not drawing current constantly. Your #8 cord is perfect. Just look at the Cord that came attached to the welder, it's probably #10.
 
   / Welder Extension Cord #27  
Last edited:
   / Welder Extension Cord #28  
60 amp Canadian is 40 amps US :). THHN wire #8 is rated 40 amps @ 60C (140F) which is how they rate extension cords. If you use the 90C tables, it goes to 59 amps, but no one recognizes that temp range for cables.


Please explain how your amps are different.

40 A US, should be 40 A Canadian.
 
   / Welder Extension Cord #29  
Yes, required by code to ground all metal bits, plus a very good idea.

JJ, #8 is used for ~50A circuits, not 80A. This is a standard welder extension cord. I can buy the exact cord with the 50A M&F plug ends on it from Hobart at the Fleet Farm store here. For home use, it is hard to get something that really needs more than 50A, and even harder to drive a welder hard enough to max that out. Home welders just don't run that hot and heavy. Not many interstate bridges built in home garages...

Use this calculator and tell me what it calculates for a 50 ft wire, and 80 amps. Should compute at #8 wire

Wire Size Calculator

This is what Lincoln says, 230VAC Single Phase 70 Amps #8




120V/40A = #10 wire.

208V/40A = #12


Pro Cut-80

K1581-1 98

208/230/460/ 1-ph: 96/87/48A (44.5)
 
Last edited:
   / Welder Extension Cord #30  
well that calculator is clearly wrong.
 

Tractor & Equipment Auctions

2020 Barreto 20RTK 36in Stand-On Trencher (A49461)
2020 Barreto 20RTK...
2015 MACK GU713 DAYCAB (INOPERABLE) (A50854)
2015 MACK GU713...
1982 LeeBoy Motor Grader (A51039)
1982 LeeBoy Motor...
Lincoln Electric Vantage 300 Welder/Generator (A49461)
Lincoln Electric...
2017 FREIGHTLINER M2 S/A SWEEPER TRUCK (A51406)
2017 FREIGHTLINER...
2003 Big Tex 10PI 16ft. T/A Pipe Top Utility Trailer (A49461)
2003 Big Tex 10PI...
 
Top