Pole barn is 145 feet from the main panel. I was hoping that # 2 aluminum would be okay with a 90 amp breaker feeding the sub panal at the building?
Pole barn is 145 feet from the main panel. I was hoping that # 2 aluminum would be okay with a 90 amp breaker feeding the sub panal at the building?
You will be fine,, If you draw 60 amps your voltage drop is about 2.5v
American Wire Gauge table and AWG Electrical Current Load Limits with skin depth frequencies
Pipe size is fine and breaker size is good,, One thing you might want to do is run a 3 wire switch loop along with the feeders so you can turn a barn light or tractor heater on from the house..