OK, i cant stand quiet any longer hehe
i AM a licensed electrical contractor...28 years now and counting.
As i stated previously, its all due to voltage drop. The room might only be 70 feet away, but if 3 rooms are wired together, then the wires are Daisy chained around all 3 rooms to the master bedroom. If all 3 rooms are say 10x10 plus the bathroom, you can easily have a run totaling 120 - 200 foot long when you add all the lengths of wire between outlets together. This is no 1.4 volt drop,
Using a true voltage drop distance of 150 feet (better guess than 70 feet in a daisy chain setup) i calculate an 11% voltage drop.
Mind you after 85 feet , there is a 5% voltage drop with #12 copper wire. But 5% is an acceptable level.
If i were you, i would run (or hire someone to run) a separate 20 amp circuit with #12 wires to a dedicated receptacle and call it good.
Without a clamp on amp tester, your just guessing. I have actual line testing equipment that cost me nearly $1,000 and with this you can actually SEE the drop in the current under load. A electrical test meter wont show you much, especially the starting load. A basic clamp on meter with a built in high test lock mode will help.
i AM a licensed electrical contractor...28 years now and counting.
As i stated previously, its all due to voltage drop. The room might only be 70 feet away, but if 3 rooms are wired together, then the wires are Daisy chained around all 3 rooms to the master bedroom. If all 3 rooms are say 10x10 plus the bathroom, you can easily have a run totaling 120 - 200 foot long when you add all the lengths of wire between outlets together. This is no 1.4 volt drop,
Using a true voltage drop distance of 150 feet (better guess than 70 feet in a daisy chain setup) i calculate an 11% voltage drop.
Mind you after 85 feet , there is a 5% voltage drop with #12 copper wire. But 5% is an acceptable level.
If i were you, i would run (or hire someone to run) a separate 20 amp circuit with #12 wires to a dedicated receptacle and call it good.
Without a clamp on amp tester, your just guessing. I have actual line testing equipment that cost me nearly $1,000 and with this you can actually SEE the drop in the current under load. A electrical test meter wont show you much, especially the starting load. A basic clamp on meter with a built in high test lock mode will help.