I hang my head and try to say this again for all to listen or ignore (Jpc gets it ) If you disconect the neutral to ground jumper on the jenny.... You loose the ground conductor from the genny to the house during a fault. QUOTE]
I don't think that is so, the neutral (aka "grounded conductor) and the (equipment) grounding conductor are bonded at the house panel, the fault current will re-enter the neutral back to the jenny's winding here.
Yes. A longer path, so some potential will develop on gen chassis -- but no alarming amt unless there is a
connection or
conductor fault.
...As to this stuf about low resistance paths: short and/or large wires are extremely low resistance. Small Fractions of an ohm. In any functioning setup where all 4 conductors make their respective contacts there is always a low enuf resistance current path to blow breakers and keep case potentials safely low in a fault. It is the contacts that are of paramount importance and that should be monitored if they are not bolted. Since a resistance at a contact is concentrated at a single point
any significant amount will heat it enuf to cause a degrading chain reaction. That is why plug connections are frowned on. You cant trust people to be aware. However, if you are you clean, and then spot check the plug under significant 120/240 loads and assure that relative temp is 0 or
very small in relation to that of the wire. And you further know that this only proves 3 out of 4. The ground contact is not proven since it is not carrying current. Best to bring a pigtail out and bolt it.
larry