daybreak1998
Silver Member
Howdy,
Here is a cut and paste from another PTO generator manufacturer
............................
GENERATOR AC NEUTRAL CONNECTIONS
The generator is shipped from the factory with the neutral ungrounded. (Neutral floating, i.e.; no electrical connection between neutral and ground connection).
The required status of the neutral depends on how the PTO generator is to be used. The NEC (National Electrical Code) requires the following.
*Emergency Supply for a Fixed Wiring System -This is the case when the PTO is used to provide emergency backup power for a fixed wiring system. This requires the output of the generator to be connected to electrical load though a double-throw transfer switch. The neutral is NOT to be connected to the ground terminal. This is how the PTO generator is supplied from the factory, no changes are required.
*Separately Derived Source --This is the case when the PTO generator is to supply only loads connected by cords plugged into the outlets or fuel capacity connector. This is the case when the load is not normally supplied by the Utility source or is not part of a fixed wiring system.
The neutral is to be connected to the ground terminal in the control panel.
1. Remove the control panel cover.
2. Locate the #4 AWG wire loop on the ground terminal.
3. Disconnect one end of the wire loop and attach it to the neutral connection terminal.
4. Tighten the retaining nuts on both terminals.
5. Replace the control panel cover and secure the fasteners.
GROUNDING THE GENERATOR
The National Electrical Code requires that the frame and external electrically conductive parts of this generator be properly connected to an approved earth ground. Local electrical codes may also require proper grounding of the unit. For that purpose, a GROUNDING LUG (Figure 13) is provided on the unit. Generally, connecting a No. 6 AWG (American Wire Gauge) stranded copper wire to the grounding lug and to an earth driven copper or brass grounding rod (electrode) provides adequate protection against electrical shock. However, local codes may vary widely. Consult with a local electrician for grounding requirements in your area.
DANGER Do not connect the grounding wire to any pipe that carries flammable or explosive substances fire or an explosion may result.
Proper grounding of the generator will help prevent electrical shock in the event of a ground fault condition in the generator or in connected electrical devices. Proper grounding also helps dissipate static electricity, which often builds up in ungrounded devices.
...............................
The emergency supply for a fixed wiring system is where you want to be. Unless you are hard wiring it in your system. What type of outlet does the PTO generator have?
I use the modular anderson connectors with mine, with all 4 wires in place. Known as a full power plug.
Here is a cut and paste from another PTO generator manufacturer
............................
GENERATOR AC NEUTRAL CONNECTIONS
The generator is shipped from the factory with the neutral ungrounded. (Neutral floating, i.e.; no electrical connection between neutral and ground connection).
The required status of the neutral depends on how the PTO generator is to be used. The NEC (National Electrical Code) requires the following.
*Emergency Supply for a Fixed Wiring System -This is the case when the PTO is used to provide emergency backup power for a fixed wiring system. This requires the output of the generator to be connected to electrical load though a double-throw transfer switch. The neutral is NOT to be connected to the ground terminal. This is how the PTO generator is supplied from the factory, no changes are required.
*Separately Derived Source --This is the case when the PTO generator is to supply only loads connected by cords plugged into the outlets or fuel capacity connector. This is the case when the load is not normally supplied by the Utility source or is not part of a fixed wiring system.
The neutral is to be connected to the ground terminal in the control panel.
1. Remove the control panel cover.
2. Locate the #4 AWG wire loop on the ground terminal.
3. Disconnect one end of the wire loop and attach it to the neutral connection terminal.
4. Tighten the retaining nuts on both terminals.
5. Replace the control panel cover and secure the fasteners.
GROUNDING THE GENERATOR
The National Electrical Code requires that the frame and external electrically conductive parts of this generator be properly connected to an approved earth ground. Local electrical codes may also require proper grounding of the unit. For that purpose, a GROUNDING LUG (Figure 13) is provided on the unit. Generally, connecting a No. 6 AWG (American Wire Gauge) stranded copper wire to the grounding lug and to an earth driven copper or brass grounding rod (electrode) provides adequate protection against electrical shock. However, local codes may vary widely. Consult with a local electrician for grounding requirements in your area.
DANGER Do not connect the grounding wire to any pipe that carries flammable or explosive substances fire or an explosion may result.
Proper grounding of the generator will help prevent electrical shock in the event of a ground fault condition in the generator or in connected electrical devices. Proper grounding also helps dissipate static electricity, which often builds up in ungrounded devices.
...............................
The emergency supply for a fixed wiring system is where you want to be. Unless you are hard wiring it in your system. What type of outlet does the PTO generator have?
I use the modular anderson connectors with mine, with all 4 wires in place. Known as a full power plug.