Look up how many GPM the PT's are, the more GPM, the faster the splitter. Also keep in mind that the GPM is usually at full throttle. If you idle down, it will be slower.
As to electric motors, general rule is 10 amps per HP @ 120v and 5 amps per HP @ 240v. So a true 5HP motor @ 240v should have a FLA rating in the 25ish range. But gotta watch motors. Some are listed as "compressor duty" 5HP motors, and are only 13-15 amps max. If you truly need 5HP, those arent the way to go.
A 3/4hp 110v motor should only be 7-8 amps. Certainly not 30. perhaps given the length of wire, it was up-sized to 10ga to minimize voltage loss, and thus the 30A is needed for that conductor size. Breakers arent meant to protect motors, rather the wiring.