GPintheMitten
Elite Member
- Joined
- Sep 8, 2009
- Messages
- 3,291
- Location
- Flushing, Michigan
- Tractor
- Kubota B2620 with BH65 backhoe, Ford 2N
I need to help my daughter run electric to 9 water troughs to power trough heaters for the winter in Michigan. Her heaters are 1500 watts each. That's 12.5 amps each for a total of 112.5 amps. This is going to be a challenge to do it in the most economical way. Not only are the total amps high but the runs are long. We are going to bury the wire in trenches when we install buried water lines to frost free hydrants in the same project.
I'm going to attach a rough diagram to show the placements.
I'm going to need to replace the subpanel in the barn to support this but that's not my problem. I've done that before. I'll check the exact wire gauges that supply the barn and size the feeding breaker in the main panel and the main breaker in the sub. But at first glance it looks to be pretty heavy guage aluminum but is only on a 60 amp breaker now. I'm hoping the existing wire to the subpanel will be large enough for a 150 or 125 amp subpanel. If not, I'll need to get my daughter to decrease the number of heaters. I would rather not have to re-feed the sub panel.
Anyway. The reason I'm posting, is that I could use your ideas on how best to supply all this in the pastures. Typically 10 guage will support 30 amps will will handle 2 heaters with some spare but the runs are long. I know I can up size to avoid voltage drop.
After looking at my diagram attached. How would I best supply the 4 heaters on the right (marked A, B, C, and D totalling 50 amps draw)? Run a 3 wire with ground to location A, attaching 2 to A and B, then running the other hot to C then D along with neutral and ground? The total run for the neutral would be 830 feet. This would be supplied by two, 30 amp single pull breakers (120 volt).
The group on the left totals 62.5 amps with a total of 890 feet.
I am aware of some heaters that are 1200 watts (10 amps) so that might have to factor into this.
Just as background, I know how to wire and have done several subpanels, a main panel and wired a previous house that I owned... all with permits and inspections. What I'm trying to figure out is a strategy to keep the wire costs down to a reasonable cost. I could home run a 10-2 w ground for each heater but that might not be the best way to go and may be more expensive than other options.
Sorry for long post. Ideas? Suggestions?
I'm going to attach a rough diagram to show the placements.
I'm going to need to replace the subpanel in the barn to support this but that's not my problem. I've done that before. I'll check the exact wire gauges that supply the barn and size the feeding breaker in the main panel and the main breaker in the sub. But at first glance it looks to be pretty heavy guage aluminum but is only on a 60 amp breaker now. I'm hoping the existing wire to the subpanel will be large enough for a 150 or 125 amp subpanel. If not, I'll need to get my daughter to decrease the number of heaters. I would rather not have to re-feed the sub panel.
Anyway. The reason I'm posting, is that I could use your ideas on how best to supply all this in the pastures. Typically 10 guage will support 30 amps will will handle 2 heaters with some spare but the runs are long. I know I can up size to avoid voltage drop.
After looking at my diagram attached. How would I best supply the 4 heaters on the right (marked A, B, C, and D totalling 50 amps draw)? Run a 3 wire with ground to location A, attaching 2 to A and B, then running the other hot to C then D along with neutral and ground? The total run for the neutral would be 830 feet. This would be supplied by two, 30 amp single pull breakers (120 volt).
The group on the left totals 62.5 amps with a total of 890 feet.
I am aware of some heaters that are 1200 watts (10 amps) so that might have to factor into this.
Just as background, I know how to wire and have done several subpanels, a main panel and wired a previous house that I owned... all with permits and inspections. What I'm trying to figure out is a strategy to keep the wire costs down to a reasonable cost. I could home run a 10-2 w ground for each heater but that might not be the best way to go and may be more expensive than other options.
Sorry for long post. Ideas? Suggestions?