After looking at my diagram attached. How would I best supply the 4 heaters on the right (marked A, B, C, and D totalling 50 amps draw)? Run a 3 wire with ground to location A, attaching 2 to A and B, then running the other hot to C then D along with neutral and ground? The total run for the neutral would be 830 feet. This would be supplied by two, 30 amp single pull breakers (120 volt).
I sort of skipped over the above the first time, but I think you're saying the same thing I suggested. For A, wire to leg L1, B wire to leg L2. For least voltage drop, (but 1 extra wire) run your 2 hots & Nuetral to C (on L1) & D (on L2) so that the neutral current adds to zero when both are on.
By "code" your 2-single pole, 30 amp breakers must have a 1 common tie handle, so that both shut off.