Electricians: Range wiring and breaker sizing code

   / Electricians: Range wiring and breaker sizing code #91  
Wow, this has gone 9 pages. Has anybody mentioned that he could upgrade the receptacle box and range cord to 60 amps instead of changing the breaker?
 
   / Electricians: Range wiring and breaker sizing code #92  
I think earlier he mentioned the stove or range was marked as a 40 amp device. It takes a lot less time for me to change a QO breaker than it would take me to replace receptacle, receptacle plate and range cord. And I would spend a lot more money than a $16 breaker.
 
   / Electricians: Range wiring and breaker sizing code #93  
Why would one want neutral on a 240V range?
To carry the neutral current from the electronic controls and the 120V receptacles.
Are you going to start talking again about something you don't understand and tell us a falicy that ground and neutral are the same ?
 
   / Electricians: Range wiring and breaker sizing code #94  
To carry the neutral current from the electronic controls and the 120V receptacles.
Are you going to start talking again about something you don't understand and tell us a falicy that ground and neutral are the same ?

Inspector 507 answered the question correctly long before you, in post #89.
 

Tractor & Equipment Auctions

2019 Isuzu NPR-HD 24ft. Box Truck (A50323)
2019 Isuzu NPR-HD...
2019 Bobcat E32i Mini Excavator (A50322)
2019 Bobcat E32i...
2018 CATERPILLAR 326FL EXCAVATOR (A51242)
2018 CATERPILLAR...
196046 (A50459)
196046 (A50459)
2016 Nissan Frontier Extended Cab Pickup (A50323)
2016 Nissan...
2019 Kenworth T880 T/A Wet Kit Day Cab Truck Tractor (A50323)
2019 Kenworth T880...
 
Top