Why do you want to use a kirk key setup? Its overly complicated(in my opinion, of course). Why do you need a captive key? All you need is an interlock like this Generator InterLock Kit Manual Transfer Switch to be perfectly safe. You can kill the grid power, then turn on the genny breaker, then start the genny, or you can start the genny, kill the grid power, then turn on the genny breaker. Either way, the genny and the grid power can never meet. Its not physically possible.
Can you show me a schematic as to how you'd not need two more hot wires with the kirk key setup? I'm not getting it.![]()
No new wires are needed for the kirk key setup.
One lock would go on the main breaker in the house and the other would go on a new genset breaker in the barn subpanel. They are setup so that:
1. There is only one key
2. The key cannot be removed unless the breaker is locked in the off position
So, to switch from utility to generator power you:
1. Shut off the main breaker in the house panel
2. Lock it off
3. Remove the key
4. Walk to the barn
5. Unlock the genset breaker
6. Turn it on