If I ever pour another slab I'll bond it. The thing is here we have periods of drought so severe that the concrete actually separates from contact with the earth. The poster said the concrete contractor left a rebar exposed and he tied into that. So his connection is not concrete encased. I'm old school and 250-A (3) is an addendum. I would love to get Megger readings on those grounds in say- 10-15 years- if I live that long. Hey, BTW, did you ever get a new TV?![]()
Somehow I can't see a slab or grade beam separating from the earth...that would require gravity to cease.
The connection doesn't have to be concrete encased as per NEC 250.68(C)(3)
From What Is A 'Ufer' Ground? | EC Mag
Herbert G. Ufer was a vice president and engineer at Underwriters Laboratories who assisted the U.S. military with ground-resistance problems at installations in Arizona. Ufer's findings in the 1940s proved the effectiveness of concrete-encased grounding electrodes. The military required low-resistance (5 ohms or less) ground connections for lightning protection systems installed at its ammunition and pyrotechnic storage sites at the Navajo Ordnance Depot in Flagstaff and Davis-Monthan Air Force Base in Tucson. Ufer developed the initial design for a concrete-encased grounding electrode that consisted of 1/2 inch, 20-foot-long reinforcing bars placed within and near the bottom of 2-foot-deep concrete footings for the ammunition storage buildings. Test readings over a 20-year period revealed steady resistance values of 2 to 5 ohms, which satisfied the specifications of the U.S. government at that time.