under ground wire help

   / under ground wire help #11  
I'll go with #12 that should be good enough to run the pumps and the light.

3% voltage drop and 95' of 12AWG should be good to 11.04A

If your pumps and lamp are under that, then you are good. If they are over that, 10AWG would be good for 17.5A
 
   / under ground wire help #12  
I'll go with #12 that should be good enough to run the pumps and the light.

Whoa, whoa, whoa. Pumps? As in more than one? The pump is not in your house?
Is there a blower too?
You need to calculate what the load (current) will be.
 
   / under ground wire help #13  
I'll go with #12 that should be good enough to run the pumps and the light.

You need to consider this;

The number of amperes drawn by the load is to be obtained from the manufacturer of the equipment. For motors, the current must be obtained from tables 430-148 (single-phase) and 430-150 (3-phase) of the NEC. Care must be taken to follow the guidelines of the NEC with regard to the number plugged into the calculator.

The NEC requires that for single motor installation, the current used in the calculation be 1.25 times the load current from the above mentioned tables. When more than one motor is used, the current of the largest load must be multiplied by 1.25, plus the sum of the rest.
 
   / under ground wire help #14  
I would run conduit and put your wire in that. Less chance of having to dig it back up after a rock nicks the wire that way.

Aaron Z
 
   / under ground wire help #15  
When I used to put them in most of them required we run #12-2 w/ ground.

What we did was ran a 10-2 with ground, put an outlet at the woodburner and installed a ground rod at the unit for an equipment ground. The reason we put an outlet on the outside of the unit with a disconnect (light switch inside the control cabinet) was so that we could hook up a light or other tool if we needed to and be able to kill power to the unit as a whole if we needed to. We figured we may be working on them at night and almost always it would be in the winter when it would be cold and probably with the ground being muddy or snow covered and we wouldn't have to go in the house to kill or energize the circuit.
And since we were an HVAC company we didn't do any underground electric other than these wood boilers and we'd buy a large spool of 10-2 underground wire that would cover anything we ever needed to do, and we usually put them in for farmers notorious for adding on to an existing circuit where a circuit was already ran. Often time the owner would build some sort of structure nearby to house wood under which had lights for working in the dark.
 
   / under ground wire help #16  
I would run conduit and put your wire in that. Less chance of having to dig it back up after a rock nicks the wire that way.

Aaron Z
Or run the UF wire and your insulated piping all in the same 4" corrugated drain.
 
   / under ground wire help
  • Thread Starter
#17  
Or run the UF wire and your insulated piping all in the same 4" corrugated drain.

The 5 " drain tile is filled with foam no room to put it in.I looked at the boiler plate is rated for 120 volts so I picked up a 100 ' of 12/3 with ground.
 
Last edited:

Tractor & Equipment Auctions

2011 Chevrolet Equinox SUV (A53424)
2011 Chevrolet...
40' CONTAINER (A51244)
40' CONTAINER (A51244)
2006 FREIGHTLINER CL120 DAY CAB (A53426)
2006 FREIGHTLINER...
Chery 7' 35 Drawer Workbench (A50120)
Chery 7' 35 Drawer...
Ford F-450 Utility Truck (A55218)
Ford F-450 Utility...
2002 WACKER RD25 ROLLER (A54607)
2002 WACKER RD25...
 
Top