A panel of some sort. I will be there tomorrow so can look closer at meter, open panel and get more info. Thanks for the help.
Since this subject came up, I need help also. We are building new house and shop and want to run single phase 300 amp service from meter 425 feet underground. Want 200 for the house and 100 for shop. What size wire do we need? Thanks
To further drive the point home- Home Depot has 1 1/2" pvc conduit listed for $0.62/ft or about $112 for the run-they don't list 1 1/4" on the website.
To have 4 8 ga wires (1000' of wire) is $274. 4 wires gets you 2+ circuits and or 240v.
Total $384 plus conduit ends.
The direct bury 10/2 romex is $175 The non outdoor rated (that's all HD had listed) 8/2 was $375 plus conduit ends. Direct bury is more!
So for about the same price as direct bury romex that only gets you one or two circuits and no 240v option you can have multiple circuits (double the power/amps of the romex) and 240v. Plus the conduit is big enough to upgrade the wires for anything you would want to do in the future. You have to dig the trench anyway- might as well use the conduit.
The meter is very near the transformer, and all the service is underground so yes the 425' is after the meter. To make matters worse our 8 acres is in a HOA. The developer had all the infrastructure done upfront,city water, phone. No NG,only buried propane tanks are allowed.
I would probably look at a 400A sevice. The extra cost for what you are planning would be minimal. This would also allow you plenty of room for future. Also find the largest panel you can. One person mentioned a 30cct panel. You will find that this does not have enough room for the circuits you will want. Things like fridges, freezers, microwaves, and most large appliances require their own dedicated circuit. There are also a specific number of outlets allowed on any circuit. The larger the house the more circuits will be used just for outlets.
The heat and AC loads also make a difference. What kind of heat will you have? Base board heaters will also use up spaces in the panel, compared to something like a heat pump that only uses a couple of spaces. There are rules in NEC and CEC that will help calculate this.
Since this subject came up, I need help also. We are building new house and shop and want to run single phase 300 amp service from meter 425 feet underground. Want 200 for the house and 100 for shop. What size wire do we need? Thanks