I have an LG mini-split 18K BTU. The A/C shop wanted about 2K to install it so I installed it myself. I bought a vacuum pump and a digital vacuum gauge. The digital vacuum gauge is important, the analog ones will not show you how low the pressure is accurately enough and they really need to be down around 300-500 microns. It's important to get all the moisture out of the lines. If you don't the oil will react with the moisture to form an acid which will be circulated through out your closed A/C system and corrode the coil, compressor, and lines from the inside, meaning the unit will not last long. To determine the BTUs you need, you will have to do a heat load calculation. If you don't you'll probably be either over or under what you need. Under means it won't provide the heating or cooling you need. Over is not good either because it won't remove the humidity from the air and consumes more power. (However, Over is better than under since you can add a separate dehumidifier.) And as mentioned earlier, with its inverter it will adjust down to what is needed for cooling fairly efficiently but "right sized" is best and most efficient. "Rule of Thumb" is not a good plan for this, but you don't need "Manual J" calcs either, you can find heat load calcs on the i-net. I used a small pump and let it run most of the day to get down to 300 microns, then released the freon. It's been running 2.5 years now and only needed the filters cleaned and the coils cleaned.
My unit came precharged for 25' lines. I needed 22' so I put an S curve in to take up excess length so I would not have to adjust the freon charge. The most difficult part of the installation is holding the 35# inside unit up in the air while trying to get the 2 freon lines, 1 drain line, and electric cable thru a 2.5" hole in the wall - 2 senior citizens were doing this. I recommend 2 younger folks or assistance from a 3rd senior citizen. Otherwise, 1 person can install one of these units.