There is no problems with a multi-wire branch circuit that is wired correctly. I wired homes for 18 years using many of these. No problem with any of them. If they are wired correctly.
The ground/neutral bond should only happen at the main service entrance. Everywhere downstream of that, ie, sub-panels, neutral and ground are to be kept separate.
Code calls for ground rods at outbuildings. That only applies to a feeder, where there is a panel and multiple circuits in the outbuilding. If it's a branch (ie, single circuit hanging off your main panel) then ground rods are not required.
I don't see a ground wire from the house out to the barn sub-panel. Just two hot one neutral for 100 amp 240 service. Does that change anything?
I know the barn was wired by amateurs some 55 years ago, and I think electricity was added to the existing house in the 1920's. An outlet tester at some locations shows combinations of lights that aren't on the list of good/bad responses.
I had to remedy something that made the chrome-plated kitchen percolator tingle when touched. That could have been deadly if someone added a longer cord and filled it at the faucet while plugged in. I suspect electricity bleeding to ground somewhere was the cause of major pipe corrosion, galvanic action, that seems to have ended after I got a few things wired like they should be.
This farmhouse is out in the country, never had a building inspector sign off anything. Dad's advice was just bulldoze the place when he was gone, too much was beyond repair. Now I'm getting old and telling the same thing to my kids. It's a cute little farmhouse (and outbuildings) but everything needs attention continually to stay functional.
Shared neutrals can be real fun when a 2 or 3 pole breaker isn't used when trouble shooting, till you figure it out. Yes, way back on commercial work a shared neutral was allowed on 3 phase. Tied handle breakers were also not required. I believe the current code requires separate neutrals on all circuits. When computers started to proliferate in the working world those shared neutrals ruined a lot of computers. We then started specifying separate neutrals even though code allowed. Shortly it became a trade practice.
Ron
This is correct but, code also requires 4 wires run to the sub-panel, 2 hots, 1 neutral and 1 ground. If you've only run 3 wires, 2 hots and a neutral, run a 4th wire if you can easily. If you can't, bond the panel.
Here's the risk/issue that you're dealing with, the ground wire is for fault current. We always say that electricity want's to find the quickest path to ground but, it's really trying to find the quickest path to it's source. If you don't have the 4th wire or the bonding screw installed, you're relying on the conductivity of the Earth as your fault current carrier back to the ground rod at the meter pole, and that's not a good bet. More likely, you're going to become the fault current carrier in some way.
The code does allow 3 wire service to an outbuilding if you run the wire in metallic conduit that is connected to both panels and acting as the ground carrier.
Thats odd. I guess they dont enforce national electric code in your neck of the woods. Technically its ok as thats how it was done for years, but this has not been a legal way to do it for quite awhile.I just put in a new home this past summer, 2017, service goes to meter out front and 200 amp breaker with small panel, then to house 200 amp panel box 320 feet away, then another 100 feet to 100 amp panel for garage. 3 wire to everything, two 8’ ground rods at each panel, and every panel is neutral ground bonded.
Thats odd. I guess they dont enforce national electric code in your neck of the woods. Technically its ok as thats how it was done for years, but this has not been a legal way to do it for quite awhile.
Bonding screw? I don't think I have one. This Federal Pacific 100 amp sub-panel in the barn was installed about 1966 but it might have been a used salvage panel at that time, Dad was 'frugal'.[responding to this prior post]
Unless they ran it in metallic conduit that is bonded to both panels and acting as the ground conductor, you need to either run a 4th conductor (the correct fix) or install the bonding screw. While not compliant withe newer versions of the code, installing the bonding screw will eliminate the risk.