STx
Veteran Member
- Joined
- Oct 13, 2014
- Messages
- 1,132
- Location
- Bandera, Tx
- Tractor
- New Holland TC40 DA, Deere 17D, Hyster SX50 forklift, Case D450, Kubota ZD1011-54, International Dump Truck, Kubota SVL-952S, Volovo EC250DL
If the neutrals and grounds are going into the same buss, you're ok. It sounds like that's what you've got.Bonding screw? I don't think I have one. This Federal Pacific 100 amp sub-panel in the barn was installed about 1966 but it might have been a used salvage panel at that time, Dad was 'frugal'.
As I noted in the prior post the panel is fed by two hots and a neutral, no ground wire, then has its own good (recently replaced) grounding rod. All the neutral wires within go to the same neutral bussbar as does the grounding rod - and also a couple of green wires from circuits added later. (nearly all the sub-circuits are two-wire).
I assume this shared neutral/ground bussbar has the same effect as a bonding screw between neutral and ground in newer construction.
Is this scheme merely obsolete or a real immediate problem?
If the aren't, run a piece of #6 copper to connect the 2 separate busses.