Locate buried electric line?

   / Locate buried electric line? #61  
When I use one where it will be exposed to the weather directly, I add a piece of weatherproof sealing tape over the top and side seams between the box and cover. 'In Use' covers are still the weak point though and do not fully prevent moisture such as wind driven rain or snow, dew, frost, etc.

I had read some previous information that GFCIs expire over time and should be replaced the same as smoke detectors and surge suppressors. I've searched since this thread appeared and can't find any definitive statement either way now.
Cant imagine a gfi going bad with time, unless something mechanical gets stuck.
 
   / Locate buried electric line? #63  
OP hasn't given us much to work on as far as I can see. Most light poles aren't very far from a building, usually not over 100' or so. I've never seen a wire take the scenic route between two points unless there are a lot of obstacles. It shouldn't be that difficult to start at one end or the other and work back along the route.

That said, you NEVER make a slice on an AC line underground unprotected. NEVER. If it ever becomes necessary, you use a properly rate box or splice case.

At this point, I'd forget about the old cable and run a new piece of UF.
 
   / Locate buried electric line? #65  
Thank you for posting the link...

GFCI are something I deal with all the time... Hospital and Property Management
 
   / Locate buried electric line? #66  
Every done electric line work,overhead distribution,transmission,fault locating or underground ? I did for 39 years, and can tell you I NEVER seen any one locate a underground fault using witching sticks.You need the proper fault locating equipment to locate a electric fault.

Nobody has said they could find a fault that way. It works for me; but, the indication is only there is a buried wire not whether energized.

Ron
 
   / Locate buried electric line? #67  
Cant imagine a gfi going bad with time, unless something mechanical gets stuck.

They do if installed outside. Changed out few in my life. Moisture corrodes the interiors. Same thing happens to switches and receptacle. Coastal areas are the worst. There is a new one out that is sealed and purported to be impervious to moisture. Haven't seen one yet. The older ones I always tried ti install inside and extend the circuit to the outdoor outlet.

Ron
 
   / Locate buried electric line? #68  
First I would check that it is a wire fault and not a fault at the lamp that is causing the GFCI to trip. Disconnect everything at the lamp and reset the GFCI, if it still trips then you have a wire fault.

I'm assuming this is direct burial wire that was done 12 inches deep using the exemption for GFCI protected circuits. It's the cheapest, least reliable method. Accept that you got your money's worth and bury a new wire. Direct burial wire is about 30 cents a foot at Home Depot. Or you could put PVC conduit in the same 12" trench for only a few dollars more and get more life out of it.

If you don't feel like doing that you may be able to cobble together something that kind of works. Your GFCI is tripping because either your line or your neutral conductor is leaking to ground. You can use an ohmmeter with everything disconnected at both ends to see which conductors are leaking. They could be leaking to the ground conductor, or they could be leaking to the actual ground. The best scenario is if one of them is leaking to the ground conductor. In a GFCI circuit the ground is unnecessary. Disconnect the ground conductor at both ends, tape it until it goes into the Romex insulation, and your leak is fixed.

If both are leaking there is no fix without digging up the wire.

If one is leaking to ground-- or the line and neutral are leaking to each other -- you might be able to cobble it. Counting the ground there are three conductors in the cable, and a GFCI circuit only needs two conductors to function properly. If you can identify which one is leaking -- and there is only one leaking -- you could rewire it. Use the non-leaking conductor as the line and the ground as the neutral. The ground needs to be insulated with electrical tape at both ends so it doesn't touch anything. If the white and black are leaking to each other whichever one you don't use needs to be taped off at both ends so it doesn't touch anything.

I would not recommend taking out the GFCI, it's essential protection for a shallow-buried cable.

I wouldn't recommend trying to find the splice and dig it up, by the time you find it you might as well have dug a new trench, and you'll end up with a repair you'll be going back to again in a few years.
 
   / Locate buried electric line? #69  
Nobody has said they could find a fault that way. It works for me; but, the indication is only there is a buried wire not whether energized.

Ron
Why witch the wire if you cannot find the fault what does that accomplish?I think the OP knew where the wire was.He was trying to find a fault in the wire.
 
   / Locate buried electric line? #70  
Why witch the wire if you cannot find the fault what does that accomplish?I think the OP knew where the wire was.He was trying to find a fault in the wire.
Because just like any other thread here on TBN, people veer off course from the OP intent. :rolleyes:
 

Tractor & Equipment Auctions

2007 National RV Dolphin 35FT Class A Motorhome (A51694)
2007 National RV...
2021 Ford F-250 XL 4x4 Ext. Cab Pickup Truck (A52377)
2021 Ford F-250 XL...
2016 Ford F-550 Palfinger PSC3216 4,000LB 2 Ton Crane Service Truck (A51692)
2016 Ford F-550...
2007 FORD F-550 XL SUPER DUTY DUMP TRUCK (A51406)
2007 FORD F-550 XL...
New Wolverine Skid Steer Forks Attachment (A53002)
New Wolverine Skid...
(1) HD 24ft Free Standing Corral Panel (A51573)
(1) HD 24ft Free...
 
Top