Advice on Generator Backup Wiring

   / Advice on Generator Backup Wiring #1  

adeoghert

New member
Joined
Jun 3, 2010
Messages
14
I need advice on how to wire up my generator to my house.

The house has already installed a manual transfer switch the services a sub panel for critical circuits. The main panel and sub panel are in the basement and the wire for the backup generator runs into the garage.

During our last outage I realized that using a 5kw watt generator I could not get a lot of the circuits powered even though the usage was less than 1kw.

Today I found out a few things
The transfer switch is wired for 240v, I suspect that I only power one half the way the connection is currently set up.
I have 3 wires (red, black, white) and a naked ground from the transfer switch to the generator hookup, but at connection box, red connected to white, black to black and the white to green (see image).

My question is what changes I need to make.

My thoughts are to change from a 3 wire black/white/green to a 4 wire black/red/white/green with the connection similar to what we have from the switch and the naked ground connected to green.
 

Attachments

  • 1.jpg
    1.jpg
    261.1 KB · Views: 98
  • 2.jpg
    2.jpg
    223.5 KB · Views: 115
  • 3.jpg
    3.jpg
    185.3 KB · Views: 104
  • 4.jpg
    4.jpg
    371.5 KB · Views: 118
   / Advice on Generator Backup Wiring #2  
The box you show is probably wired for the 240v but either without the neutral (somewhat normal) or without the ground (not so good).

You don’t really explain what the “box” is or does. Nor do you tell us what your gen is- 240v or 120v.

Based on you lack of knowledge on the subject I’d be inclined to suggest you phone a friend or hire an electrician to help you out.
 
   / Advice on Generator Backup Wiring #3  
Based on you lack of knowledge on the subject I’d be inclined to suggest you phone a friend or hire an electrician to help you out.

From what I read,I concur with that statement.
 
   / Advice on Generator Backup Wiring
  • Thread Starter
#4  
You don稚 really explain what the 澱ox is or does. Nor do you tell us what your gen is- 240v or 120v.

Box is in garage where connection to generator is made, changeover switch is in the basement 30 ft away.

4a.jpg
 
   / Advice on Generator Backup Wiring #5  
Box is in garage where connection to generator is made, changeover switch is in the basement 30 ft away.

View attachment 614731
Coming from the generator looks to be two blacks and a dirty white. From the transfer switch a black, a red, a white and a ground. I would not connect like that but it really depends on how it is connected at the generator. I would keep white to white, black to black and the other black to red. Actually I would get matching wire colors. I suggest an electrician, there is not enough information here. Who made this connection? Is your generator 240V?
 
   / Advice on Generator Backup Wiring
  • Thread Starter
#6  
Coming from the generator looks to be two blacks and a dirty white. From the transfer switch a black, a red, a white and a ground. I would not connect like that but it really depends on how it is connected at the generator. I would keep white to white, black to black and the other black to red. Actually I would get matching wire colors. I suggest an electrician, there is not enough information here. Who made this connection? Is your generator 240V?

The generator is 120/240v

If you look at the transfer switch, it is a 240V switch. There are two black live wires and a white neutral for the line and for the aux we have a black and red live wires and a white neutral.
 

Attachments

  • 1a.jpg
    1a.jpg
    2 MB · Views: 83
  • 2a.jpg
    2a.jpg
    1.8 MB · Views: 93
   / Advice on Generator Backup Wiring #7  
Nothing needs to be changed, buy yourself HARBOR freight multimeter. What we can't see is the connection at the generator. When the Gen is running find out what two wires give you 240. since you only have three wires. They will line1, line 2, neutral, the generator will not be grounded.
 
   / Advice on Generator Backup Wiring #8  
You need a 4 wire flexible cord and a 4 prong male plug that connects to the generator receptacle. Not sure what the person who wired this was thinking. What should be the neutral (dirty white conductor) coming from the generator is jumpered to what is presumably a hot conductor, which should give you a short. I suspect the black wire that connects to the white conductor is connected to the neutral prong on the plug you have now. I'd like to see how the plug end of the 3 wire cord you have now was connected. I wouldn't use this setup until you get it corrected. Also would be good to see a picture of the generator receptacle.
 
   / Advice on Generator Backup Wiring
  • Thread Starter
#9  
I have been using this connection with a portable generator both using a 5-15 plug and an L14-30 plug.

Former owner used a 25Kw PTO generator with a 6-50
 
   / Advice on Generator Backup Wiring #10  
Green or bare, ground,

white wire should be neutral,

red wire should be hot,

Black wire should be hot,

Hot to neutral should be 110/120 volts, hot to hot should be about 220/240,

ground to neutral , should be 0 volts, hot to ground should 110/120 volts,

since I don't know how other things are wired,

post 4 , looks like a neutral and a hot is miss wired,

but looks to me like you need some one who knows what is going on, to help you out, before you fry some thing,
 

Tractor & Equipment Auctions

2016 VOLVO VNL300 TANDEM AXLE DAY CAB (A52576)
2016 VOLVO VNL300...
PREVIEW DATES AND TIMES (A51573)
PREVIEW DATES AND...
Deere 9970 Cotton Picker (A52748)
Deere 9970 Cotton...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
2009 Freightliner Columbia 120 Winch Truck, VIN # 1FUBA5CK39DAM2731 (A51572)
2009 Freightliner...
2018 Lexus IS300 Sedan (A51694)
2018 Lexus IS300...
 
Top