It does, but it also shows a 50 amp plug for 220 volts.Doesn't that page for the 210 say it'll pull 24amps at 230V?
And the 200 says 19 amps at 240V?
It does, but it also shows a 50 amp plug for 220 volts.Doesn't that page for the 210 say it'll pull 24amps at 230V?
And the 200 says 19 amps at 240V?
#8 copper THHN wire is good for 55 amps. You will need to look at the manual for the welder to see how many amps it draws. AND REMEMBER, THE BREAKERS IN THE PANEL ARE FOR PROTECTING THE WIRE ONLY. THE BREAKERS ARE NOT FOR PROTECTING ANYTHING CONNECTED TO THE WIRING. Also, it doesn't matter how thick the metal you are going to weld is, the wire supplying power the welder must have the ampacity equal to or greater than the maximum amps the machine is rated for.All, question on wiring and breaker for my personal use small garage.
I have a 50 amp circuit from my house to the garage on 6/3 wire (black, red, white and ground).
I planned to wire a 30 amp circuit for welding with 8/3 wire, but is that enough for say a Hobart Handler 210MVP or a Mult-Handler 200 Multiprocess? I wouldn’t ever need to weld anything thicker than 3/8”.
Handler® 210 MVP™ MIG Welder | HobartWelders
Multi-Handler 200 Multiprocess Welder | HobartWelders
Will a 30 amp circuit with 8/3 work?
I understand that the breaker protects the wiring of the circuit.#8 copper THHN wire is good for 55 amps. You will need to look at the manual for the welder to see how many amps it draws. AND REMEMBER, THE BREAKERS IN THE PANEL ARE FOR PROTECTING THE WIRE ONLY. THE BREAKERS ARE NOT FOR PROTECTING ANYTHING CONNECTED TO THE WIRING. Also, it doesn't matter how thick the metal you are going to weld is, the wire supplying power the welder must have the ampacity equal to or greater than the maximum amps the machine is rated for.
Eric
It does, but it also shows a 50 amp plug for 220 volts.
I wrote about THHN specifically, because it seems to be the most common single strand wire, the wire most likely to be found at the local hardware store or home improvement store. Anyway, check out this link: THHN/THWN-2 Copper Wire | WireAndCableYourWay.comI understand that the breaker protects the wiring of the circuit.
Where would I find chart that shows # 8 copper can handle 55 amps? I thought # 6 was only rated for 50 amps.