Im wiring the whole garage from the beginning.Yep. If I had a 110/220 capable welder, and I was going to run a new circuit, I'd just go with the 220 circuit.
Will a 30 amp circuit with 8/3 work? yes, but if inspected it may get a correction notice.All, question on wiring and breaker for my personal use small garage.
I have a 50 amp circuit from my house to the garage on 6/3 wire (black, red, white and ground).
I planned to wire a 30 amp circuit for welding with 8/3 wire, but is that enough for say a Hobart Handler 210MVP or a Mult-Handler 200 Multiprocess? I wouldn’t ever need to weld anything thicker than 3/8”.
Handler® 210 MVP™ MIG Welder | HobartWelders
Multi-Handler 200 Multiprocess Welder | HobartWelders
Will a 30 amp circuit with 8/3 work?
Pardon me not understanding your first comment.Will a 30 amp circuit with 8/3 work? yes, but if inspected it may get a correction notice.
MVP 210 gives a minimum conductor size as #14 copper (see note 4 on sheet), but must be rated for 75 degree C. Which would limit you to individual conductors in conduit. Or MC cable concealed in a wall if it is exposed to physical damage.
HOB Multi-Handler gives a minimum conductor size of #12 copper (See note 5 on sheet) Or MC cable concealed in a wall if exposed to damage.
This will get you by an inspector if this is being inspected.
Personally, I would use the 240 volt option with #12 thhn in conduit with a 30 amp breaker for the Multi handler. Your mileage may vary?
Same for the MVP 210, but use a 25 amp breaker. Again, your mileage may vary?
Up the breaker size to the next size if they trip.
View attachment 807229View attachment 807240
Why would larger cable be cause for a correction notice? Because it is rated for 60 degree C per Art 334.80.Pardon me not understanding your first comment.
Why would larger cable be cause for a correction notice?
Note the wires are inside the walls.
There not looking at the oversized wire, but the 60 degree C rating for the wire. When a lot of welder manufacturers specify 75 degree C (or higher rating) wire for branch and feeder circuits to welders as the only wiring method allowed.Also NATIONAL ELECTRIC CODE (NEC) has special section for welding circuits that differ from your electric stove, air compressor, electric drier, well pump circuits.... Hard to believe a inspector would ding a installation for over sized wire....