The simplest answer is "Because that is what the code requires"So I am not trying to be argumentative, but what no one has answered is why. I know there is a good reason but I have yet to understand it.
See: Why do we need to bond neutral & ground in breaker boxIn the box white and copper. (neutral and ground) are tied to the same spot. Yes there are two different terminal strips but the both are attached to the wire leading to the grounding rod.
So if there is a fault with an incorrect 2 wire 110 hookup(meaning neutral and ground on the same wire) what is the danger. If hot where to contact neutral the current would still ind up at the ground in the box.
From there:
The "neutral" is technically called the "grounded" conductor. It is grounded by ground rods at the utility transformer by the utility. We must ground it also at the service entrance, which can be at either or both the meter and main switch, technically called the Service Disconnecting Means.
Most panels, such as you refer to as the Main Breaker Box, has the main switch in it. It is at this point the neutral is grounded by connecting to a grounding electrode.
Sidebar to confuse you, if the main switch is ahead of the panel, such as outside at the meter, the grounding and bonding of the neutral is done at the main switch, not at the panel.
It is from this point the neutral must be separate from any other grounding, and must be separate from the equipment grounding conductor (bare or green wire) in any branch circuit. Since the neutral is the return for any 120 volt circuit, it is a current carrying conductor. The bare or green wire of each branch circuit is reserved to only carry current back from a circuit if there is a ground fault (short circuit).
The equipment grounding conductor is intended to be reserved to be ready to carry any fault current back from a short circuit, in an effort to allow the current to rise quickly to trip the circuit breaker for the circuit with the problem.
This acts as a safety/redendant return for a circuit. Connection of the neutral/ground at the main switch insures that all neutrals and grounds are now at the same earth potential, and the equipment ground is created, or begins.
Since a "subpanel" is downstream from the main switch, it is considered as a branch circuit, and is treated the same as a branch circuit, separate and insulated neutral return for any 120 volt circuits, and a separate equipment ground for any metal, such as the panelbox.
A neutral can be touched with no fear of injury, as it is at zero earth potential, because it has been grounded.