I'm not an electrician so forgive my ignorance, but I have been told that 4-wire is only needed IF the appliance has 220v AND 110v circuits within it. Like a stove that has 220 heating elements and a 110v digital display.
But things such as a compressor or welder that are 220 ONLY, 3-wire is okay??
There is no ignorance to forgive....You are 100% correct on all counts. I AM a master electrician, and an electrical engineer, and there is so much BS on this thread it is funny. What the OP is proposing is OK. A sub panel does not need a neutral if you are only supplying line to line loads. A service needs a neutral, even if you don't need it, but it is not required to be extended beyond that point unless needed to supply line to neutral loads....which is almost always.
All you really need to do is ask the local inspector before he comes...He is right, even when he is wrong. The inspector will be so **** happy that you thought it through this far:thumbsup: