Chilly807
Elite Member
You may have to run the engine at slightly higher than 2200 rpm before it's loaded. When you load a mechanical governor it inherently causes the speed to "droop" as the load increases. With a generator this results in reduced frequency, which the heat pump may not tolerate for starting. Speed droop is defined as "a decrease in speed setting for an increase in load". I doubt you have engine power issues if the tractor is operating normally otherwise.
In other words, instead of having a solid 60 Hz as you would off the utility grid, the frequency from your generator may be quite low as the load increases.
I'd recommend hooking up a multi-meter that will read frequency, and check the generator voltage and frequency output at 540 PTO speed. If the tach isn't correct, you may have less than 60 Hz to begin with, or if the voltage regulator is out of adjustment you may be trying to start the pump with lower than normal voltage too.
Both are correctable in most cases, the frequency surely is. If the voltage is correct, adjust the engine speed to give you 61 Hz with no load, then try starting the heat pump and see what happens. Ideally you will have 60 Hz at 50% of the generator maximum load capacity, the upper and lower end will be what they are unless you adjust the engine speed to give you 60 Hz at a steady load.
Sean
In other words, instead of having a solid 60 Hz as you would off the utility grid, the frequency from your generator may be quite low as the load increases.
I'd recommend hooking up a multi-meter that will read frequency, and check the generator voltage and frequency output at 540 PTO speed. If the tach isn't correct, you may have less than 60 Hz to begin with, or if the voltage regulator is out of adjustment you may be trying to start the pump with lower than normal voltage too.
Both are correctable in most cases, the frequency surely is. If the voltage is correct, adjust the engine speed to give you 61 Hz with no load, then try starting the heat pump and see what happens. Ideally you will have 60 Hz at 50% of the generator maximum load capacity, the upper and lower end will be what they are unless you adjust the engine speed to give you 60 Hz at a steady load.
Sean