drm, again many thx for your valuable input. I appreciate the explanation of the hilti failure pattern as it helps me visualize your suggested rebar plan.
My homegrown pier reinf plan is essentially the same as yours except I planned #4 rebar for the verticals circled by #3, mostly because I can do the bends myself. The #4 verticals would then tie in to the #4 slab crisscross pattern, with 4' spacing. Only one question in this matter...would the "90deg hooks" be 90deg bends on the vertical rebar, inward toward the anchor area, so as to intersect the projected failure region, yet not interfere with hilti placement?
No need to apologize for your disclaimer, it just adds a professional touch.
Chris, I don't know what I did to deserve such advice either, but I have found the TBN forum in general to be a class act, in terms of both advisors and advisees. I posted questions along these lines in a couple popular construction/contractor forums, but the advice received here is considerably more useful (as I suspected it would be based on my tractor exchanges). Theres some good folk in this place. I'm an electronics engr by trade so I'm soaking up all this materials and civil engr advice.
With my limited experience I agree with your foundation assessment. I was surprised the plans specified a pier vice monolithic foundation (as were the concrete contractors who bid on finishing the slab).
Chris, just to clarify "screed form or two"...do you mean temporary screed pipes/wood which break up the expanse of the 24x36 into manageable screed sections, then pulled out prior to finish? Can you recommend what sort of pipes/support works best? Good advice on the garage door, thx.
Marty, the risk with the grind plan is, unless I'm way off on measurements, chances are the anchor would take up a portion of the hole needed for the hilti.
I haven't excavated for the piers yet, but I've dug a 20in deep trench for the electrical. At that depth the soil was hard clay and appeared virgin. I do understand that even hard clay will absorb water, contract and expand, so I'm using a 3/4 minus gravel base for cushion.
I did some research on the 5/8" Kwik Bolt II hiltis. A published report shows allowable tension at 3100lbs (with SI), 1600lbs (w/o SI), and 3100lbs shear, all at 4in depth with 4000psi concrete. The Special Investigation (SI) includes verification of drill bit compliance, hole depth, cleanliness, concrete compressive strength, and verification of proper install procedure. Trying to figure out how this compares with standard 10 or 12in 5/8" anchors.