Cable size

   / Cable size #1  

daedong

Veteran Member
Joined
Jul 8, 2003
Messages
1,265
Location
South Australia
I have a large inverter on my houseboat. I have run (Twin) double 00 cable to the battery box. in the box i want to put a fuse block however the fuse block i have will only take one cable would it be acceptable to reduce back to one cable before going into and out of the fuse block.
 
   / Cable size
  • Thread Starter
#3  
Ron,

The fuse i have is very similar to that one .

My inverter required 0000 cable which i was unable to get so as ran TWO 00 cables to get cable capacity. However my fuse will not accommodate two cables so i wondered if I could reduce back to a single cable for about 2 inches either side going in and out of the fuse
 
   / Cable size #4  
Reducing from two 00 to one will make the single 00 cable the smallest point in your wiring. You will not be able to draw enough current through a single 00. Other than cost. Why not use 2 fuse holders. One on each 00 line. Each holder would have a fuse 1/2 total amperage.
What size inverter do you have? My 5000 watt inverter has 00 for a 10' run.
 
   / Cable size #5  
Ron H. is right, you need 2 fuse blocks.

If you use 2 fuse blocks be sure you use fuses rated for 1/2 the amperage load.

Bill Tolle
 
   / Cable size #6  
I think they are giving you some good advice on using 2 fuse blocks.
 

Tractor & Equipment Auctions

2019 TIGERCAT 234B TANDEM AXLE DE LIMBER (A54607)
2019 TIGERCAT 234B...
AUCTION STARTS HERE @ 9AM (A52706)
AUCTION STARTS...
2022 Toro Workman 07921 Electric Utility Cart (A51694)
2022 Toro Workman...
9202 (A50322)
9202 (A50322)
2004 TRAILKING 101" X 53' STEP DECK TRAILER (A50459)
2004 TRAILKING...
Caterpillar Loader Quick Coupler (A55218)
Caterpillar Loader...
 
Top