The chimney is right at the peak of the roof and is about 4.5' above the roof line
 
/ chimney problems #22  
I was talking about the stove pipe ,from the stove to the chimney(between the stove and chimney)
 
/ chimney problems #23  
1. make sure that all the stove pipe joints are tight we want no room air going in the chimney.
2. make sure the pipe is in the chimney flush with the tile and that it is cemented in, we want no room air going in to the chimney.
3. look at your clean out door if their are any air leaks, check it with a match run it around any gaps or cracks if it sucks it in duct tape it shut.
4. if you can build hotter samller fires avoid loading it up and closing down the air.
5. If you put your stove therm on the stove pipe 1' away from the flue collar you should have 350 to 500 deg. at this temp. your chimney should stay hot enough to prevent the build up.
6. creasote will condense on the surface if is below 250 deg. The goal is to keep the chimney hot hotter is better

Is most of your build up at the top of your chimney???

Rich
 
/ chimney problems #24  
Wow, Sitting here reading this and it is really warm here in the basement. My burner has an adjustable auto damper that I have presently set so the stack runs about 350.......
 
/ chimney problems
  • Thread Starter
#25  
richh
Thanks for all the info I will check into that .
Most of the plugging is about 4 feet above the thimble and down
 

Marketplace Items

2019 Ford F-550 4x4 Dur-A-Lift DTAXS39 39ft. Bucket Truck (A60352)
2019 Ford F-550...
2019 CHEVROLET SILVERADO CREW CAB TRUCK (A59823)
2019 CHEVROLET...
2003 MAC TRAILERS 45' WALKING BOTTOM TRAILER (A60430)
2003 MAC TRAILERS...
Triple Sink Table (A60352)
Triple Sink Table...
2019 CATERPILLAR  XQ35 GENERATOR (A58214)
2019 CATERPILLAR...
SKIDDED WASTE WATER FIBERGLASS TANKS (A60736)
SKIDDED WASTE...
 
Top