Right now I all have is a Honda 5kw gas generator, original cost $2,000. I bought a Honda (not just Honda powered) because ( at that time compared to others), it produced very clean AC. Many things in my house even my furnace, has electronic/ expensive controls, so I felt it was a worthwhile investment over a $500 unit.
Years ago it wasn't uncommon for me to loose power. A few times we were out for around a week. Things have improved and I have only lost power a few times in as many years for maybe 2-3 hours each.
Every year I drain the fuel and replace it with fresh stabilized fuel, run the machine under load and change the oil. The bottom line is that the generator doesn't really require maintenance, the engine that drives it does. This year the engine failed to start. Cleaning the carb solved the problem. I didn't get 100% reliability, even maintaining things the way I do.
My theory is this. With a PTO unit, it can sit covered up in the barn, with almost zero maintenance and still
While this is a great theory and one that a lot of people believe, it does not always work in practice.
In addition to prime mover maintenance, the generator head itself must be exercised. Sitting allows the brushes and armature contact's to corrode or seize, insect's to take up residence and in rare cases a weakening of the magnetic fields.
All this results in an inoperable generator when you need it most.
I exercise my gen sets at least every 4 months by running for 30 minutes with at least 25 percent load.