Actually this is from the manufacturer of my welder, who sells a UL listed product.
<font color="blue"> Using the following instructions, have a qualified electrician connect
a receptacle (NEMA 6-50R Type) to the power lines at the fuse
box. Three #10 or larger copper wires are required if conduit is
used. For long cable runs over 100', #8 or larger wire in conduit
will be needed to prevent excessive voltage drops. Fuse the two hot
lines with 50 ampere super lag type fuses as shown in the following
diagram. The center contact in the receptacle is for the grounding
connection. A green wire in the input cable connects this contact
to the frame of the welder. This insures proper grounding of the
welder frame when the welder plug is inserted into the receptacle.
If a separate disconnect switch is used, it should have two poles for
the two hot lines and both should be fused for 50 amperes. </font>
<font color="blue"> Using the following instructions, have a qualified electrician connect
a receptacle (NEMA 6-50R Type) to the power lines at the fuse
box. Three #10 or larger copper wires are required if conduit is
used. For long cable runs over 100', #8 or larger wire in conduit
will be needed to prevent excessive voltage drops. Fuse the two hot
lines with 50 ampere super lag type fuses as shown in the following
diagram. The center contact in the receptacle is for the grounding
connection. A green wire in the input cable connects this contact
to the frame of the welder. This insures proper grounding of the
welder frame when the welder plug is inserted into the receptacle.
If a separate disconnect switch is used, it should have two poles for
the two hot lines and both should be fused for 50 amperes. </font>