Some pretty smart fellas on here.

Here is what it turned out to be:

Yes, the neutral connection at the switched recp. is strange. It is like it was wired so it could either be a direct outlet like the rest, OR switched. Thats the only reason I can think that they wired it like that. Yes, circuit 26 wires pass through that box. Maybe it was meant to be ran like that, but supposed to have separate neutrals and when the time came, they just tied the whites together cause they forgot.

But that in itself wasnt the only problem. CobyRupert hit it spot on. A neutral connection in the spare bedroom outlet came loose. Thus when the closet light was turned on, forced the current to seek the neutral path back through circuit 27 thus the 240v potential in that workbox.

MY guess, with the neutrals tied together in the switched recep, the GFI never worked from day one. Thus the amatuer that wired the house back in 1995-1996 never had anything on the load side of the GFI otherwise it would pop.

So my fix was to separate the neutral circuits in the switched box, and fix the loose neutral in the spare bedroom box. Pretty simple fix. Just took some time to figure out what is going on. I basically pulled the covers off and outlets/switches out of every box and started tracing the circuit.

Cause imagine this: If I didnt include the diagram, and all I told you was this:

when turning on the closet light on circuit 26, the GFI trips on circuit 27 taking out both circuits and allowing potential for 240v @ the GFI box, how confusing is that. And to top it off, the main cause was a loose wire in the spare beroom:confused2: Cause that is all I had to go on this morning until I started unwiring things and tracing it out.
 
   / Electrical Challenge of the Day: GFI tripping #13  
Would you call this an electrical cluster.....?:laughing:
 
   / Electrical Challenge of the Day: GFI tripping #14  
I couldn't reply from work and I see you already have your answer.
 
   / Electrical Challenge of the Day: GFI tripping #15  
that was easy. a good diagram sure helps.
 
   / Electrical Challenge of the Day: GFI tripping #16  
Just got on, the 240V tells the story, just had to find the broken neutral wire...
'
Good to see ya found it and fixed the problems. Lots of times you will find when running with a bad neutral that you blow bulbs faster or see extra bright or dim lights depending on what else is helping to make the neutral connection.

Mark
 
   / Electrical Challenge of the Day: GFI tripping #17  
sounds like it was a fairly easy fix for ya, and trouble shooting, granted pulling and moving stuff away from wall to get to outlets and like ....

winter todo list, upgrade main house panel to get rid of the 1950ish box. and re-run wiring to various outlets / lights upstairs. not really looking forward to it. half outlets upstairs no longer work, i cut and removed the wires to them due to just plain bad wire (mice chewed them up or insulation falling off), it is and still will be a nightmare of stuff i have found, that needs to be redone.
 

Tractor & Equipment Auctions

2020 Case IH 8250 4WD Combine (A50657)
2020 Case IH 8250...
TAKEUCHI TB210R EXCAVATOR (A51242)
TAKEUCHI TB210R...
2004 Ford F-250 4x4 Crew Cab Mechanic Service Truck (A49461)
2004 Ford F-250...
Informational Lot - Financing (A51039)
Informational Lot...
2018 PETERBILT 567 (A50854)
2018 PETERBILT 567...
2010 CAT 140M MOTORGRADER (A50854)
2010 CAT 140M...
 
Top