In the process of taking my cottage off is standalone solar PV electric and hooking in to my main system at the house. You can see the trench work here: http://www.tractorbynet.com/forums/kioti-owning-operating/245828-kb-2375-trench.html
I am running approx 375 ft of #2 copper from my main distribution panel to a sub panel at the cottage. 70AMP breakers, 240 volt. Loss will be just over 3%.
My question is regarding ground wire. Do I need to run 2 separate grounds panel to panel or is a single sufficient. I can buy 3 conductor w/ ground to run in my 2inch conduit. If I need the 2nd ground I suspect I'll have to run 3 separate conductors plus the 2 grounds. Naturally, the 3w/grd would be easier for me to handle. This is not a grd rod issue as there are double rod.
A friend is bringing over a copy of the NEC, but thought I'd tap into the BN brain trust.
David
I am running approx 375 ft of #2 copper from my main distribution panel to a sub panel at the cottage. 70AMP breakers, 240 volt. Loss will be just over 3%.
My question is regarding ground wire. Do I need to run 2 separate grounds panel to panel or is a single sufficient. I can buy 3 conductor w/ ground to run in my 2inch conduit. If I need the 2nd ground I suspect I'll have to run 3 separate conductors plus the 2 grounds. Naturally, the 3w/grd would be easier for me to handle. This is not a grd rod issue as there are double rod.
A friend is bringing over a copy of the NEC, but thought I'd tap into the BN brain trust.
David