Veteran Member
Hope no one misinterpreted what I did. I didn't size the cable length based solely on the 175 amps at 30 volts, but since the welder is basically a transformer or power converter, for the most part power in equals power out, (except for a little loss in internal heat). Anyway, since the 175 amps and 30 volts was all that's known, I converted this to watts and then to approximately 22 amps input at the 240 volts. If the nameplate says 30 amps at 175 volts, we'll have to recalculate. Just a note on the tables. It looks like the tables assumed copper wire. If aluminum is used instead, you'd be way off from the tables.