I agree with everything except the #10 at a continous 30 amps. For romex cable, sure. Not so much with 3 or 4 strand SO cable. 30 amps continous will burn the neutral.
I work for a generator company that provides distro along with cabling. We use 10/5 SO (90c) with our 21-20 plugs (20amps) even at a full 20 amps you can see the neutral cable charred inside the insulation.
Another thing to remember (for all the guys not electrical savy) is that a breaker has two purposes. It will trip when it heats up. A 50 amp breaker is a thermal breaker and is only good for 80% for a continuous load. It will only trip once it exceeds that 80% for an extended period. The other purpose is to provide a break point in case of a direct short (phase to phase or phase to ground). If you are using cable inadequate for the load, the breaker doesn't know, doesn't care.. So if the cable is on fire from over amperage, the breaker isn't going to trip until the insulation melts and two lines cross... We see it on a lot larger scale with our 400 amp rated 4/0 cable. The weak link is in the connection points (cam lock ends similar to stick lead extensions). If we are pulling 350-380 amps (digital breakers rated for 100% continous) and there is a weak connection point heat is created. We had a couple cam lock catch fire (just smoldering) at this years super bowl with only 200-220 amps on cable rated for 400...
Just keep that in mind.. Don't cut corners when it comes to electricity. No one here wants to see anything happen to anyones shop, house or barn