I was thinking about the above. While I don't disagree and I do follow the state's thinking, in my mind, it seems that between the generator's own 30 amp breaker and the Load Center's "30 amp generator breaker", "overload" should be impossible.
The 6.5kw gen, at full load, would be capable of 29.54 amps. A load, much beyond that, should trip "a breaker". The gen's surge capability is 8kw, which would provide 36.36 amps, which should trip a breaker.
Bottom line: It seems as if, it would be very hard to overload the generator.
who can ever second guess what they are thinking when they pass a law. They are just trying to make the world idiot proof. I think that they would force kids to wear bubble-wrap when outdoors if they thought they would get away with it. Guess they dont think anyone is capable of turning off a few breakers ??