We still are curious about your concern in terms of the bolts. let's face it, if you get winds or storms hard enough to strain those bolts, I would think other things, like the roof would be gone and the nails would have pulled out of the studs. I guess the sill plate would be in tact though.
I am rebuilding my house that burned down.
I have an existing slab with footers and this particular bolt is exactly where I need a hold-down for seismic stability.
The engineer involved wants me to drill through the foundation, and footer (all 18" of it), and then embed a 5/8" threaded rod with a nut and large washer on the end in a new footer to be poured under the existing one.
Depending on whose analysis you use we only need either 5650 or 6400 lbs. of pull out strength.
Since I already have a 5/8" x 12" anchor bolt (~9" of embedment) which was wet-set 20 years ago right at the exact spot necessary, I am questioning why I should destroy this in order to produce a kludge of a tie-down with lower strength.
Changing engineers is not possible, because this is the only remaining sticking point and I need to submit plans this week in order to get moving on the construction.
He actually isn't a bad guy, but I think he has gone overboard on this one.
From the table in the article, the existing bolt would be good for 9503 lbs of seismic pull out force if it were 3" from the edge of the footer. Unfortunately, it is only 1.5" from the edge and I now have to find how much to de-rate it for this location.
Somehow, all my engineering instincts tell me it is OK, but that I am never going to be able to prove it is OK.
So, I am now starting to look for a 3/4" x 20" long masonry drill that will fit my Bosch SDS rotary hammer. 16" ones are $39.99, which isn't bad, but I haven't found a longer one yet.
P.S. The seismic loads anticipated are real. The San Andreas fault (San Francisco 1906) is about 1/2 mile from the house.
I am rebuilding my house that burned down.
I have an existing slab with footers and this particular bolt is exactly where I need a hold-down for seismic stability.
The engineer involved wants me to drill through the foundation, and footer (all 18" of it), and then embed a 5/8" threaded rod with a nut and large washer on the end in a new footer to be poured under the existing one.
Depending on whose analysis you use we only need either 5650 or 6400 lbs. of pull out strength.
Since I already have a 5/8" x 12" anchor bolt (~9" of embedment) which was wet-set 20 years ago right at the exact spot necessary, I am questioning why I should destroy this in order to produce a kludge of a tie-down with lower strength.
Changing engineers is not possible, because this is the only remaining sticking point and I need to submit plans this week in order to get moving on the construction.
He actually isn't a bad guy, but I think he has gone overboard on this one.
From the table in the article, the existing bolt would be good for 9503 lbs of seismic pull out force if it were 3" from the edge of the footer. Unfortunately, it is only 1.5" from the edge and I now have to find how much to de-rate it for this location.
Somehow, all my engineering instincts tell me it is OK, but that I am never going to be able to prove it is OK.
So, I am now starting to look for a 3/4" x 20" long masonry drill that will fit my Bosch SDS rotary hammer. 16" ones are $39.99, which isn't bad, but I haven't found a longer one yet.
P.S. The seismic loads anticipated are real. The San Andreas fault (San Francisco 1906) is about 1/2 mile from the house.