MossRoad said:I may be wrong, but it looks like each panel has 6 single pole circuits. That means you have a maximum of 12 with the two panels, not 16.
It also looks like the installer used the factory cable to feed two units from the outside plug. It is meant for one unit. I think that exceeds the factory cable rating. The factory cable could melt before any of the breakers trip, especially if you use a generator that exceeds the cables rating.
Actually if the generator output does not exceed the amperage rating for the input cable you are OK. Some codes call for a circuit breaker on the input side to foolproof this. Usually the sum of all your individual circuits will exceed the main breaker rating - you don't expect to run everything at once.
I agree with other posters that you should remove the cover and see if the transfer switch wires were not pulled off or bypassed. The TS wiring is very simple.