Whoa! I think you mistook my meaning. The little icon I pasted is supposed to mean "confused." As in...I am confused by your answer. You described your thermostat control solution as having little to do with freezing, but you described keeping the house from freezing as one of the reasons for the solution. I figured there might be two meanings to freezing (something to do with the generator vs. the house). I was looking for clarification.
So, yes, I am guilty of ignorance, because I clearly didn't know what you meant with your freezing reference. But arrogant? For seeking clarification? Geez, I hope not.
No offense was intended. I do appreciate your comments in response to my original post.
No "confused" icon on my side. It came across as though you were less than receptive to input. Your last helped to clarify and who knows where the icons go on my end- I'm on the taptalk app on a smart phone. Half the time I can't attach photos either.
To be clear the "typical" remote start generator uses "dry contacts" to start. This is the input a "typical" remote transfer switch uses and it happens to be the same thing a "typical" low voltage thermostat uses.
So if you want your gen to run every Tuesday at 1pm simply program your thermostat to run at that time. Or if you want to maintain your auto start feature put the thermostat and transfer switch in series.
This was my biggest dilemma when sizing my propane tank with an auto start transfer switch- how can I easily control when to start and stop the generator when I'm away.....this prevents the unneeded burning of fuel. And thus, in theory, requires less storage.
I figure my needs would be to maintain some battery backups that keep some of my electronics going, my refer cold and my house at an acceptable temp. With that, I would need about an hour a day of gen run time.
If you live in a more moderate climate you may actually need more time per day to keep the refer or freezer if that's important.
If you are home you will need more time per day- as stated in my first post only you can decide that.
So in summery-
-Find the gen's specs for fuel consumption per hour
-Calculate and decide your needs per day and how many days you want the gen to run
-decide if you want a dedicated tank. If so take the stated tank volume and deduct 20% for its inherent design and another 20% because the gen will get used for weekly runs so it won't always be full.
-if you tap the existing tank the math is similar except I'd deduct 50% for usage and you will obviously want to keep the tank topped off. Murphy's Law would have an outage occur when the tank is low!
I have an ASCO automatic transfer switch with the auto start wiring in series with a thermostat and a Winco stand-by generator with Honda motor.