One well company owner told me he loves portable generators. He gets lots of business replacing well pumps every year because of undersized generators.
So, since I know that you (@grsthegreat) know so much about sizing generators, how does one appropriately size a generator to a well pump? Is it some number of kW/HP? LRA of the pump motor not more than XX% of the generator full load amps? Or?One well company owner told me he loves portable generators. He gets lots of business replacing well pumps every year because of undersized generators.
Yes, it is a great product and used more often by sailors than landlubbers for some reason. I would also point out that the autotransformer can help clean up the quality of generator power as well.Warning: Engineering opinion coming from a 400/230V land dweller
One thing to consider if you have a 220/110 generator and potentially big 110V loads is to use an autotransformer. Victron make them for the purposes of load balancing split phase systems for generator and inverter supply. Autotransformer - Victron Energy
An appropriately sized autotransformer will allow a 3kVA 110V load to be run on a 3kVA 220/110 generator for example (within reason of course)
Actually i generally never even take a well pump into consideration when installing a 22KW Generator because there wont be any effect on a well pump, even a deep water pump. Where it matters is when a customer has a 5,000 or 7,500 watt portable unit and wants to power house and well with manually flipping breakers. At this point i place a clamp on meter and log actual start and run amps that the well uses during operation. Then i also use a clamp on meter to check what amperage there wanting to run When power is out. Most of the time i can convience customer to go larger and get a 10 kw portable once they see the actual readings.So, since I know that you (@grsthegreat) know so much about sizing generators, how does one appropriately size a generator to a well pump? Is it some number of kW/HP? LRA of the pump motor not more than XX% of the generator full load amps? Or?
I have a backup well that is 2HP/240, but our main well pump is 3 phase delta 5HP. I have been thinking of getting a generator and add a VFD large enough to cover the main well, but I haven't managed to size the generator.
All the best,
Peter