Hi guys,
Thought I would add this post to the all ready long list of contributors.
Earlier in the post I commented on how one of the two circulating pumps was considerable hotter (to the touch) than the other on my system and didn't really understand why.
Well, now I know why - the warm pump was starting to fail (slowly seized up). My system shut down on low pressure and I thought that was the compressor gas safety. Well I was wrong, the low pressure shut down was for the circulating fluid in the horizontal loops. The pump that failed was the first one that starts when the system kicks in - the second one starts when auxiliary heat is called for. This is as I understand it - didn't know this before and am on a learning curve right now !
After talking with the repair tech for the company that installed my WaterFurnace unit, it was suggested I swapped the roles of the pumps around - that is the second called pump be made the first called pump. This would enable the system at least to work. I didn't want to mess with the control board as I don't understand or follow electrical diagrams too well, so I swapped the wiring to the pumps. This way the second pump would start when the system started up and the other pump that failed was left disconnected.
Well, I tried it and it worked. The system is working for moderately cold temperature and I am guessing here, probably ok to around zero degrees 0F. I have a propane furnace that I can run at the same time as the geothermal unit to enhance temperatures if need be.
During this process I did some digging and found out a bit on replacing circulating pumps and flow centres - of which I knew nothing about before. Check link below:
http://www.waterfurnace.com/literature/geolink/im1547ew.pdf
I posted it as it makes things a bit clearer on what is involved. It also describes the function of the flow centre and how it is used. Might be handy for someone who didn't know about them (like me ).
I have a couple of questions that someone might be able to answer.
After replacing a pump the recommendation is to use the illustrated circulating rig for two hours to get air out of the system. If the pump is shut off with the three way valve when installation is done, and then carefully cracked open to allow residual pressure (exerted from the loop expansion tank) to bleed any air out of the pump, would this work ? If it can be done it would allow the owner to replace his own circulating pumps if done carefully. I think the two hour minimum time for using the separation unit would be expensive (travel time to and from residence plus at least two hours on site, probably three hours) at $100 an hour.
I priced out replacement pumps and they are around $350 each as far as I can tell. I need to replace the two and not just one pump as it's mate is going to fail as well eventually. The ones in the system are well over ten years old - maybe even 15 years. so replacing just one pump would be unwise.
Just thought I would share this information as it is handy to know.
I was surprise that the HVAC tech tried to tell me that I would need a new flow centre for around $1600 plus the cost of the pumps ! Replacement pumps is all I need at present IMHO.
Would appreciate comments from those that are familiar with the geothermal systems (I have horizontal ground loops) and what would you do in my case?
Thanks