We heat and cool 2400 sqft plus 1800 heated only. Our unit is 4.5 kW producing about 18.5 kW of heating/cooling.
My observation was that during very cold windy nights (-10 to -15F) the geo run almost constantly keeping the temperature of the liquid at about 80 F. Therefore I have the temperature SP set to 80F for all heating season.
1 ton=3.5 kW=12000BTU/hour. So our geo is 18.5/3.5 = about 5 ton.
Thanks Ladia, sounds like we have similar winter conditions.
Of course several factors have to be accounted for. How well is your place insulated? Room height? Basement? R values?
For instance, I'm essentially heating 1500 sq/ft with R55 in the ceiling (14 foot height in the great room with an insulated basement. (1500 sq/ft)
If I add my workshop in I have another couple of hundred sq/ft. Right now I'm running a .75 nozzle at 140 lbs. which gives me about 106k btu's. I run about 10 to 15 minutes on the hour in cold weather so that means 106/6=17.6k btu/hr. to 106/4=26.5 btu/hr. This is why I'm thinking 2 to 3 tons the most here.
Chilly, the same for your space, it's hard to go by just sq/ft.
Rob