quicksandfarmer
Elite Member
A passive system is going to have to be far larger than a heat pump to get the same result.
Let's say you want to keep your space at 40F and your groundwater is at 45F. The heat released by a radiator (which is what your slab will be) is determined by two things: the different between the surface temperature and the air, and the are of the radiator. Let's say a typical heat pump puts out water at 110F. The most efficient case for a radiator is when the water leaves at the air temperature, that means all of the heat in the radiator is lost to the air. So in both cases the water is leaving at 40F. In the passive system it's entering at 45F and leaving at 40F, the average temperature is 42.5F. The difference between the radiator temperature and the air is 2.5F. In the heat pump case the water enters at 110F and leaves at 40F, the average temperature is 70F, the difference is 30F -- twelve times what it would be for the passive case. To get the same result, the area of the passive radiator has to be twelve times as big!
Let's look at circulator pump and piping sizing. That's determined by the drop in temperature of the water as it circulates. Passive case, it comes in at 45F and leaves at 40F, a five degree drop. Heat pump, it comes in at 110F and leaves at 40F, a seventy degree drop. The passive case needs to move 14 times as much water to get the same result, which means much bigger pumps, bigger pipes, and electricity used pumping water.
It's the same on the underground side. With the passive system you're taking water out of the ground at 45F and returning it at 40F. With the heat pump, it depends whether you have an open or closed loop. With an open loop your fluid is water and you can't chill it below freezing, so you'd be returning it around 33F. With a closed loop you can use antifreeze and return it at perhaps 15F. So your temperature delta with a heat pump is 2.5 to six times as big as with a passive system. The bigger your delta the smaller your pumps and pipes.
Let's say you want to keep your space at 40F and your groundwater is at 45F. The heat released by a radiator (which is what your slab will be) is determined by two things: the different between the surface temperature and the air, and the are of the radiator. Let's say a typical heat pump puts out water at 110F. The most efficient case for a radiator is when the water leaves at the air temperature, that means all of the heat in the radiator is lost to the air. So in both cases the water is leaving at 40F. In the passive system it's entering at 45F and leaving at 40F, the average temperature is 42.5F. The difference between the radiator temperature and the air is 2.5F. In the heat pump case the water enters at 110F and leaves at 40F, the average temperature is 70F, the difference is 30F -- twelve times what it would be for the passive case. To get the same result, the area of the passive radiator has to be twelve times as big!
Let's look at circulator pump and piping sizing. That's determined by the drop in temperature of the water as it circulates. Passive case, it comes in at 45F and leaves at 40F, a five degree drop. Heat pump, it comes in at 110F and leaves at 40F, a seventy degree drop. The passive case needs to move 14 times as much water to get the same result, which means much bigger pumps, bigger pipes, and electricity used pumping water.
It's the same on the underground side. With the passive system you're taking water out of the ground at 45F and returning it at 40F. With the heat pump, it depends whether you have an open or closed loop. With an open loop your fluid is water and you can't chill it below freezing, so you'd be returning it around 33F. With a closed loop you can use antifreeze and return it at perhaps 15F. So your temperature delta with a heat pump is 2.5 to six times as big as with a passive system. The bigger your delta the smaller your pumps and pipes.