I am not sure if I am following ya.

Right now there isn't a house or electrical service. Is the rebar ground done in lieu of the old (2 copper rods) way of grounding or is both supposed to be done?

Another thing. When grounding rebar in dairy barns for stray voltage the bar is all welded together but in the house it could be tied together. I don't see how the tied bar can be a good enough conductor.

In 2006 here, the rebar attachment was done in lieu of the ground rods. The rebar was not welded. I haven't been around new construction since then and do not know what the current local practice is.

One of the concerns about going to this here, was what happens in the case of a lightning strike. Do you blow a hole in basement wall vs. a hole in the dirt? I am not sure if anyone has ever had this problem, but would rather replace some electronics than my foundation.:confused:
 
   / Grounding the foundation rerod?
  • Thread Starter
#12  
I got the scoop on things. They still want 2 ground rods as well as the foundation rods.
 
   / Grounding the foundation rerod? #13  
In NC when I did my garage, since I put rebar in the pad I had to bring out a wire and attached that to my electrical ground and put in a ground round in the ground just outside the garage. The 4 wire feed from the house included my house ground, which tied into the ground system for the house.

Using a pad as a means of grounding sounds like a really bad idea. Concrete does conduct electricity, but not very well compared to wire. I like to think of my pad as a great big anti-static mat. When I was pulling up plastic on the pad I had down for painting, I got a nice static zap when I touched the pad surface.

Just for fun, I took an ohm meter and measured from my AC ground in the garage to a point about 4' in from the edge of the pad. I had to puncture the seal on the concrete with the point of the probe.

I initially got a resistance of 10 megohms. I mostened the contact point (ok, I spit on it :laughing:) and got a resistance of 2 megohms. So if you think of concrete with bonded/grounded rebar like a piece of wire, it's not very good.

There is a concept of "Ohms per square" when you have a sheet or surface material. If I exposed a 6 inch square of the concrete and put a metal plate on it and then measured the resistance, it would be much lower than the point contact measurement I made. Even lower still if the contact area (note: _area_ not _point_ contact) was wet (don't ask how that would happen :laughing:).

The ohms per square concept is odd in that if you took a good sized area (like my 30'x40' pad) you would get the same resistance with the point probes 6" apart as you would 3' apart. Even though the probes are further away, there are now even more possible paths for the current to flow.

So if the pad were in contact with the ground, it would be a low enough resistance to pass some current, certainly enough to shock or kill someone touching a live wire. If the pad is on gravel, even if it's wet, there is still the ability to pass current but it's a pretty poor ground.

So a pad with rebar connected to your AC ground (and thus your ground rod(s)) is a good deal and it protect you from huge voltages developing along the pad if there was a lightning strike near by on the ground or on the building. Of course, this is lightning so all bets are off, YMMV, etc.

Pete
 

Tractor & Equipment Auctions

2019 ALLMAND NIGHT-LIFE V SERIES LIGHT PLANT (A52706)
2019 ALLMAND...
2013 MACK ELITE LEU613 GARBAGE TRUCK (A51406)
2013 MACK ELITE...
2012 Ram 3500 Crew Cab Flat Bed Truck (A53422)
2012 Ram 3500 Crew...
2013 FORD F450 XL SUPER DUTY BUCKET TRUCK (A51406)
2013 FORD F450 XL...
2013 Cadillac ATS Sedan (A53424)
2013 Cadillac ATS...
2002 VOLVO L150E WHEEL LOADER (A51246)
2002 VOLVO L150E...
 
Top